Results 1 to 10 of 10
    9
    Default Moving Cold Water Ground
    I currently have a ground wire running from my service panel to the incoming cold water pipe in my basement. This is a bare copper wire in metal conduit.
    My question is this:
    I would like to re-route this ground due to a remodel. Do I have to use the bare copper in conduit or is there another option out there that is easier to work with such as a copper wire in plastic sheathing, etc?
    Denver, CO
    666
    Default Re: Moving Cold Water Ground
    The simple answer is that if is #6 or larger is does not need to be in conduit in exposed locations. Regardless of size if it is not exposed to physical damage (Inside the house** it does not need to be in conduit.
    However, it can not be spliced and must be "continuous"
    Electrical PVC and fittings are a great way to protect the wire in exposed locations and a plus is that PVC does not need to be bonded since it is a non-conductor.
    Dec 2008
    Kentvw made some good points but the ground wire can be spliced, it is in the NEC under an exception in the grounding chapter. It can be spliced but only by irreversable crimp type connectors (usually called hi-press. Or where it attaches to ground bars in panels.
    6,023
    Use only a continuous wire. Although it may be an exception in the NEC it may not be allowed by local code. As one inspector told me "I don't care what the NEC says, this is what we require." And the one thing I have learned is the inspector is always right.
    9
    Thanks for the help guys.
    I believe I will just disconnect the ground from the cold water, pull the wire through the conduit and re-route it without any conduit at all since this is in the house and is not exposed to the elements.
    731
    Quote Originally Posted by simon View Post
    i think you should check with your code authority first before doing JUST what you said to modify your system not maintenance or repair. exposed to the elements outdoors not the same issue as exposed to potential physical damage inside the finished or unfinished basement. do you understand what bonding means?
    Shamokin, Pa.
    645
    I agree 100%. I have been told the same as well. And guess what, you say "Thank You" and do just that.
    Denver, CO
    666
    Actually, jga77 was 100% correct in his post.... So I stand corrected.
    2008 NEC
    "250.64 Grounding Electrode Conductor Installation.
    Grounding electrode conductors at the service, at each
    building or structure where supplied by a feeder(s) or
    branch circuit(s), or at a separately derived system shall be
    installed as specified in 250.64(A) through (F).
    (A) Aluminum or Copper-Clad Aluminum Conductors.
    Bare aluminum or copper-clad aluminum grounding conductors
    shall not be used where in direct contact with masonry
    or the earth or where subject to corrosive conditions.
    Where used outside, aluminum or copper-clad aluminum
    grounding conductors shall not be terminated within
    450 mm (18 in.) of the earth.
    (B) Securing and Protection Against Physical Damage.
    Where exposed, a grounding electrode conductor or its enclosure
    shall be securely fastened to the surface on which it
    is carried. A 4 AWG or larger copper or aluminum grounding
    electrode conductor shall be protected where exposed to
    physical damage. A 6 AWG grounding electrode conductor
    that is free from exposure to physical damage shall be permitted
    to be run along the surface of the building construction
    without metal covering or protection where it is securely
    fastened to the construction; otherwise, it shall be in
    rigid metal conduit, intermediate metal conduit, rigid nonmetallic
    conduit, electrical metallic tubing, or cable armor.
    Grounding electrode conductors smaller than 6 AWG shall be
    in rigid metal conduit, intermediate metal conduit, rigid nonmetallic
    (C) Continuous. Grounding electrode conductor(s) shall
    be installed in one continuous length without a splice or
    joint except as permitted in (1) and (2):
    (1) Splicing shall be permitted only by irreversible
    compression-type connectors listed as grounding and
    bonding equipment or by the exothermic welding process.
    (2) Sections of busbars shall be permitted to be connected
    together to form a grounding electrode conductor."
    The issue, as I see it; few people other than electrical contractors and their trained employees neither have the access or the knowledege to effectivly use these types of tooling and splicing methods.
    9
    I have no reason to splice the wire so I am good there.
    I will check out the electrical PVC option though for extra protection.
    Thanks guys.
    731
    Thanks guys.
    sounds like a good plan and you're welcome.