+ Reply to Thread
Results 1 to 4 of 4
  1. #1
    Join Date
    Mar 2010
    Posts
    1

    Red face New Outdoor GFCI Outlet

    I have a 110 outlet in the garage and want to add a new GFCI outlet outside that area to run a fountain in the yard.

    Can I continue the wiring from the existing inside 110 outlet, out through the wall, through a Schedule 40 PVC conduit to a new GVCI-protected receptacle with cover?

    Or do I need to run a completely new line from the circuit box clear outside?

  2. #2
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,941

    Default Re: New Outdoor GFCI Outlet

    The receptacle in the garage should be a GFCI you could then run the wiring off the load side of it and both receptacles would be GFCI protected.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  3. #3
    Join Date
    Aug 2007
    Posts
    7,593

    Default Re: New Outdoor GFCI Outlet

    As Jack points out, the garage should already be GFI protected. If this is the case, then continuing the line out and installing a standard receptacle would be appropriate. The way to find out is to check both the main service and all other wet locations for either a GFI breaker (main panel ) or a GFI outlet.

    GFI's are generally located in a garage, in bathrooms, in kitchens, or at exterior outlets. A single GFI can be responsible for all other wet locations, so don't assume that because you see a standard receptacle that it's not GFI protected. Conversely, don't assume that a standard receptacle is automatically protected, regardless of the presence of other GFI devices in the home. The only way to be sure is to inspect all outlets and circuits and test the various outlets which should be protected, i.e. any location prone to moisture or near a water source.
    I suffer from CDO ... Its like OCD, but in alphabetical order, LIKE IT SHOULD BE!!!

  4. #4
    Join Date
    Jun 2007
    Location
    Shamokin, Pa.
    Posts
    645

    Default Re: New Outdoor GFCI Outlet

    Quote Originally Posted by JayNFran View Post
    I have a 110 outlet in the garage and want to add a new GFCI outlet outside that area to run a fountain in the yard.

    Can I continue the wiring from the existing inside 110 outlet, out through the wall, through a Schedule 40 PVC conduit to a new GVCI-protected receptacle with cover?

    Or do I need to run a completely new line from the circuit box clear outside?
    If any part on the PVC is above ground and exposed to damage use Schedule 80 PVC, per NEC 300.5{D**{4**.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •