    Quote Originally Posted by ZZZ View Post
    If you have two 120 volt, 15amp heaters on seperate poles for example, with a shared neutral, the current on the neutral would be zero amps. The same would go for incandescant lamps or any other purely resistive loads.
    Theoritically ..... only if the loads on the 2 legs are perfectly balanced ... which is unlikely in real world applications.


    As far as damage from a bad connection on the neutral, it is not as likely as damage from a bad connection on the line where the most amperage is flowing. This is why most burned connections are on the main breaker and not on the service neutral.
    On branch circuits sharing neutral electronic equipment can be damaged without necessarily seeing burned connections on the main breaker.
    "" an ounce of perception -- a pound of obscure "
    - Rush

  2. #12
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,023

    Default Re: How to break up a circuit with a shared neutral?

    Although balanced loads or nearly balanced loads work, I always recommend against shared neutral in a residential application. As and example one circuit feeds the bathroom which has a vent fan, a ceiling light, a vanity light, etc. When every thing is on the draw is say 12 amps. Ont the other branch you have an attic vent fan drawing 12 amps. every thing is OK until the neutral break or bad connection, and you have one 60 watt light on in the bath and the vent fan is running. Now you are running 240 volts through the circuit, dropping 220+ volts on the fan and 18+ volts on the light and the circuit is drawing over 22 amps. A 20 amp breaker may or may not trip and you will burn out the light or the attic fan. It's very difficult to maintain balance loads in a residential application.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  3. #13
    Join Date
    Jun 2007
    Location
    Shamokin, Pa.
    Posts
    645

    Default Re: How to break up a circuit with a shared neutral?

    Quote Originally Posted by canuk View Post
    Theoritically ..... only if the loads on the 2 legs are perfectly balanced ... which is unlikely in real world applications.


    On branch circuits sharing neutral electronic equipment can be damaged without necessarily seeing burned connections on the main breaker.
    Unlikely in the real world, but not uncommon.

  4. #14
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: How to break up a circuit with a shared neutral?

    Generally speaking the multiwire branch circuits ( MWBC ) are safe and fine to use providing everything is wired correctly. As I mentioned earlier the service to the home is the same thing ( shared neutral ) without giving it a second thought.

    Personally I like to wire most circuits with a seperate neutral but there are times when convienience comes into play and I'lll use the MWBC for lights only.
    This way I'd rather have the 240 split on light bulbs than having 180 volts running through my DVD player.
    "" an ounce of perception -- a pound of obscure "
    - Rush

  5. #15
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,023

    Default Re: How to break up a circuit with a shared neutral?

    Quote Originally Posted by ZZZ View Post
    Jack,
    You are correct also, it will very likely damage something if you lose the neutral due to the higher than normal voltage that results. I do not like using them in residential either. I was just trying to clear up the originator's fear of high neutral currents, which will never be higher than the highest line current at any time. Changing one conductor to a ground is a very good idea also.
    Nonetheless, is still acceptable and approved to use multiwire branch circuits. On the other hand, it would not bother me a bit if the NEC bans them at some point. It is not necessary to balance the load in these applications either, but it is always good practice. Don't forget, the service to a residence it using a shared neutral for two lines and no one would ever ask for an additional neutral for it.
    So true, sub panels also, however my concern is that it is many times more likely to have a connection problem with the application of a wire nut than a terminal connection and it's more likely to be done by an armature than the service connections.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  6. #16
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: How to break up a circuit with a shared neutral?

    Quote Originally Posted by Ernie_Fergler View Post
    Unlikely in the real world, but not uncommon.
    Yep ..... pretty smart coal cracker
    "" an ounce of perception -- a pound of obscure "
    - Rush

  7. #17
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: How to break up a circuit with a shared neutral?

    Jack ... that's no reason to condem MWBC rather consider the consequences when it.s done improperly .... as with anything electrical.
    "" an ounce of perception -- a pound of obscure "
    - Rush

  8. #18
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,023

    Default Re: How to break up a circuit with a shared neutral?

    Quote Originally Posted by ZZZ View Post
    Are they worse than amatures?: )

    I dislike them especially because of the double or triple pole breaker requirement, you have to shut down additional circuits to work on them. Worse,if you don't have them (like in his house) you can be electrocuted by the opening the neutral not knowing it has a second feed.
    It's not nice to make fun of senior citizen's mistypes. Besides it's spelled amateurs.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  9. #19
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,023

    Default Re: How to break up a circuit with a shared neutral?

    But it just doesn't seem to help with "Old-timers" disease.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  10. #20
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: How to break up a circuit with a shared neutral?

    Quote Originally Posted by ZZZ View Post
    Are they worse than amatures?: )

    I dislike them especially because of the double or triple pole breaker requirement, you have to shut down additional circuits to work on them. Worse,if you don't have them (like in his house) you can be electrocuted by the opening the neutral not knowing it has a second feed.
    Wouldn't that be the reason for the breakers?
    Last edited by canuk; 09-19-2008 at 10:10 PM.