  1. #21
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,774

    Default Re: Can someone explain the difference between phases and poles??

    Quote Originally Posted by kentvw View Post
    I wish member djohns would sound in here because distribution is his gig but he’s been working a ton of hours in LA.

    As far as phase angles go my guess is that it has a lot to do with how a utility distributes power and the types of transformers they use.

    My office is fed overhead with three phase and three pole set transformers feed our service from three overhead phases that I know are 120 degrees apart.

    The city block is fed from lines that run down the alley. One half is commercial three phase but the other side of the block is residential single phase.

    If you look down the alley each single phase house service is fed with one “pot” or transformer fed with two alternating phases as in AB, next BC, next AC and so on.

    Given that I know that each houses service has two hots that are 120 degrees apart. This means that the transformers are fed off of a three phase delta supply.

    NOTE HERE:
    If your having trouble understanding electric speak just think of it this way:
    A generator rotates in a full circle and a full circle contains 360 degrees. So for three phase draw a triangle inside of the circle. That is the symbol for “delta” . Then 360 divided by 3 is 120 degrees. Each point were the triangle meets the circle is where the generator is tapped to send power out to the distribution system

    Keep in mind that you can tap a winding anywhere you want and ground it. For single phase it is a center tap as has been pointed out here. The “neutral” is not carried on the transmission lines. It is created by center tapping the transformers secondary winding and grounding it.

    rabbitgun
    In an industrial area, where three phase is avalible the main lines are delta supplied, but once you get away from industrail areas the feed is generally 2 wire, so at a distrabution station the delta supply is split and becomes 3 single phase high voltage supplies to different residential areas. In other words AB goes one way, BC goes another , and AC a third direction.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  2. #22
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,774

    Default Re: Can someone explain the difference between phases and poles??

    Quote Originally Posted by canuk View Post
    Jack ... I get what you're saying .... I did one mistake there is no phase shift between the primary and the secondary.
    the way I figure it we are using two 120 volt supplies in series to produce the 240 volts along with the center tap to drain the difference between the 2 unbalanced loads which creates a split phase.
    Which would be aiding ( boosting ) each other resulting in the 240 volts.

    This means that one split 120 volt leg would have to be 180 degrees out of phase with the other 120 volt leg. Otherwise they would be opposing ( bucking ) each other resulting in 0 volts.

    So mathematically the polar equation :

    (120v @ 0degree) minus (- 120v @180 degree) = 240 v @ 0degree.

    Just a thought.
    Ok, look at this way there is no phase in DC voltage, If you take two 1.5 v batteries, connect in series and connect the center connection to ground. It looks like a + and - 1.5 volt power supply. It reads + 1.5v from center to top and -1.5v center to bottom and reads 3 volts top to bottom. They are in phase no phase shift, the lower voltage (just like the 120vac) appears to be shifted but it's not, it's just that we use a refferance point, ground to take the readings.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  3. #23
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,774

    Default Re: Can someone explain the difference between phases and poles??

    Quote Originally Posted by rickpantel View Post
    Well....I started this thread with my question, and I am totally overwhelmed with the depth of knowledge of the members responding. Thanks to all who have responded!

    Bsum1 said it well...holy mackerel, you guys are very knowledgable indeed!

    So...here is a photo of the power pole and transformer outside my house (see attached). Obviously, the very top wire is the high-voltage line...somebody said it was about 7000 volts or so. This I assume is the single phase distribution from the power grid. The transformer is obvious with the 3 lines for distribution to the houses (2 split single phase hots and a center-tap neutral)....so far so good. I get it this far.

    What I can't understand is why there is only one high-voltage line at the top of the pole. The schematic diagrams drawn earlier show the primary winding of the transformer with two wires on the high voltage side...where is this second wire? Rabbitgun alluded to this by saying that the neutral is not carried on the transmission lines, but I don't understand how this is possible.

    Any takers?
    It would appear that you have a grounded high voltage system coming to the transformer. In other words it is using ground for the return. I have never seen that around here.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  4. #24
    Join Date
    Aug 2007
    Location
    The deep South
    Posts
    459

    Default Re: Can someone explain the difference between phases and poles??

    The picture is a bit strange in that there is no neutral conductor on the primary . Not something that is done here for sure .

    As far as transformer connections go , here is a good source of info . Kinda dated , but still good .

    http://www.mhprofessional.com/downlo...67890_ch15.pdf

  5. #25
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,774

    Default Re: Can someone explain the difference between phases and poles??

    By the way as a point of referance.
    A delta transformer is a three winding transformer with the windings wired so the form a ▲.
    A Whye transformer is a three winding transformer with the windings wired so the form a "Y".
    Both are for 3 outputs and there would be absolutely no reason to ever use either for residential power.
    A step down 2 output transformer is a transformer that steps the voltage down. For instance a residential transformer that has a 7000 volts input and 2 outputs of 120 volts each.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  6. #26
    Join Date
    Jan 2008
    Location
    Lakeland ,MN
    Posts
    356

    Default Re: Can someone explain the difference between phases and poles??

    Quote Originally Posted by JLMCDANIEL View Post
    By the way as a point of referance.
    A delta transformer is a three winding transformer with the windings wired so the form a ▲.
    A Whye transformer is a three winding transformer with the windings wired so the form a "Y".
    Both are for 3 outputs and there would be absolutely no reason to ever use either for residential power.
    A step down 2 output transformer is a transformer that steps the voltage down. For instance a residential transformer that has a 7000 volts input and 2 outputs of 120 volts each.
    Jack
    Jack I would be the first to say I do not know utility installations.

    A Y transfomer is for instance 120 volts on each of the three phases. since the other end of all three phases are tied together and then grounded phase to phase is 1.73 of each phase. Thus 208 volts is measured from any two phases. the same senerio above is used on 277/480 volt system.

    A delta 3 phase is 240 volts measured at each detal connection. To get 120 volts they center tap one of the windings hence the 120 volts.

    I seen your drawing in the other post with the pump.Using a single phase tap off of a utility pole feeding a transformer. How do they make the phase shift if it is 180 degress out of phase as you described? A capacitor or inductor? they shift the voltage only 90 degrees? I want to learn something new here
    Harry

  7. #27
    Join Date
    Aug 2007
    Location
    The deep South
    Posts
    459

    Default Re: Can someone explain the difference between phases and poles??

    Quote Originally Posted by djohns View Post
    The picture is a bit strange in that there is no neutral conductor on the primary . Not something that is done here for sure .

    As far as transformer connections go , here is a good source of info . Kinda dated , but still good .

    http://www.mhprofessional.com/downlo...67890_ch15.pdf

    Start reading at section 15.9 and you will see the schematics . It'll make sense then .

  8. #28
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,774

    Default Re: Can someone explain the difference between phases and poles??

    Quote Originally Posted by Ravens53 View Post
    Jack I would be the first to say I do not know utility installations.

    A Y transfomer is for instance 120 volts on each of the three phases. since the other end of all three phases are tied together and then grounded phase to phase is 1.73 of each phase. Thus 208 volts is measured from any two phases. the same senerio above is used on 277/480 volt system.

    A delta 3 phase is 240 volts measured at each detal connection. To get 120 volts they center tap one of the windings hence the 120 volts.

    I seen your drawing in the other post with the pump.Using a single phase tap off of a utility pole feeding a transformer. How do they make the phase shift if it is 180 degress out of phase as you described? A capacitor or inductor? they shift the voltage only 90 degrees? I want to learn something new here
    Harry,
    As I said there is no phase shift, no 180 degree shift, no 90 degree shift, it is single phase. It appears that there is a phase shift if you connect an O scope reference to ground . If you connect the O scope leads to display the two other legs of the transformer, it appears that as the sign wave goes up for the top leg it is going down equally (180 degrees) on the bottom leg but that is only because you are using the center tap as your reference point. If you use the bottom leg as the reference and hooked the leads to the center and top of the secondary the display would show the top going up to 240 RMS and the center going up th 120 RMS at the same time (in phase). Although you can get the appearance of a phase shift referencing to the center tap there is in fact no shift.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  9. #29
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: Can someone explain the difference between phases and poles??

    Quote Originally Posted by JLMCDANIEL View Post
    Harry,
    As I said there is no phase shift, no 180 degree shift, no 90 degree shift, it is single phase. It appears that there is a phase shift if you connect an O scope reference to ground . If you connect the O scope leads to display the two other legs of the transformer, it appears that as the sign wave goes up for the top leg it is going down equally (180 degrees) on the bottom leg but that is only because you are using the center tap as your reference point. If you use the bottom leg as the reference and hooked the leads to the center and top of the secondary the display would show the top going up to 240 RMS and the center going up th 120 RMS at the same time (in phase). Although you can get the appearance of a phase shift referencing to the center tap there is in fact no shift.
    Jack
    Jack .... that's the point .... with reference to ground ( neutral) there is a split in the phases.

    If you look at the attached schematic .... this represents the secondary side of the transformer .... also the mains power in the home.

    Here is where the (+) and (-) polarity markings really become important ..... so it is clear whether they are aiding (“boosting”) each other or opposing (“bucking”) each other. You can see the split-phase sources in the schematic (each 120 volts @ 0 degrees), with polarity marks (+) to (-) just like series-aiding batteries can be used to represent this.


    If we mark the two sources' common connection point (the neutral wire) with the same polarity mark (-), you have to express their relative phase shifts as being 180 degrees apart. Otherwise the two voltage sources would be in direct opposition with each other, which would give 0 volts between the two “hot” conductors.

    Power systems in North American households and light industry are most often of the split-phase variety, providing the 120/240 VAC power. The term “split-phase” merely refers to the split-voltage supply in such a system.

    . By definition ....
    A split-phase power system is one with multiple (in-phase) AC voltage sources connected in series, delivering power to loads at more than one voltage, with more than two wires. They are used primarily to achieve balance between system efficiency (low conductor currents) and safety (low load voltages).

    Basically ... this kind of AC power supply is called "single phase" because both voltage waveforms are in phase, or in step, with each other.
    Single phase power systems are defined by having an AC source with only one voltage waveform.


    Is it any wonder why I used to fall asleep in theory class.
    "" an ounce of perception -- a pound of obscure "
    - Rush

  10. #30
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,774

    Default Re: Can someone explain the difference between phases and poles??

    Canuk,
    Wake Kent up.
    There is a significant difference between split phase and phase shift. Because the windings are in the same direction the phase pattern of the two windings are identical. If you ground the bottom line rather than the center tap and you read from the bottom line you would see the center tap to 120 RMS and the top leg go to 240 RMS at exactly the same time, reverse at the same time and go to the same RMS value in the opposite direction. That's because it is single phase. Because you change you reference point does not create a phase shift.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb