    Default Re: Circuit Breaker

    Glad you got it figured out, and thank you for coming back and updating your progress. It helps us to diagnose similar issues in the future.

  2. #12
    Join Date
    Aug 2007
    Location
    Denver, CO
    Posts
    666

    Default Re: Circuit Breaker

    Yup, thanks for the update.

    However.............

    Most panels are numbered; Top left #1, top right #2. Down the left side will be 1, 3, 5, and so on. Down the right side will be 2, 4, 6 and so on. On a single phase panel 1 and 2 are on phase A, 3 and 4 on phase B, 5 and 6 on phase A. The rows alternate between A and B phases.

    You have said #3 and #5 were the two breakers feeding the same circuit but based on what I described above that would mean A phase and B phase were feeding the same circuit, which, would be a dead short.

  3. #13
    Join Date
    Jun 2007
    Location
    Chicago, IL
    Posts
    162

    Default Re: Circuit Breaker

    Except, of course, on a Pushmatic panel, which has phase A on the left side & phase B on the right side.

    Oddest looking double-pole breakers that you'll ever see.
    HTH

    Dave

  4. #14

    Default Re: Circuit Breaker

    It kind of sounds like it may be double fed.