Results 1 to 10 of 11
Thread: Open Ground
    Jun 2008
    5
    Question Open Ground
    I have an outlet with an open ground. What could happen if it remains open?
    5,773
    Default Re: Open Ground
    Probably nothing if your using it for appliances with 2 pronged plugs. If you use it for electronic equipment with a 3 prong plug the filtering and safety protection won't work. If you plus a tool with a 3 prong plug into it and the hot wire is shorted to the case you could get electrocuted.
    Lakeland ,MN
    356
    In my opinion a ground is probably the most important wire in a modern wiring installation. A ground is used to carry a fault current back to the main service and draw maximum current which then causes the circuit breaker to trip or fuse to open. That being said the fault must be directed to the ground by either a three prong male plug in the appliance cord. That ground wire must be grounded to the metal frame of the appliance and or electrical device ground path. But as Jack Stated if there is only a two prong cord it is not used.
    Having a three prong outlet that has no ground is giving a false indication that a ground is present. It typically is a easy fix I would suggest you take time and pull the outlet and check.
    Turn off the power and see if there is a bare or green wire attached to the outlet. if it is check to make sure it is connected to the other ground wires and tight.
    If that does not fix your problem come on back and we will help.
    Harry
    Yep .... great post Ravens53.
    Jun 2008
    5
    Quote Originally Posted by Ravens53 View Post
    No third wire. I thought that the box was ground (used a volt meter with a prong in the hot and the other on the plate screw), but when I replaced the 2-prong with a 3-prong it wasn't grounded. Actually, it was grounded the first time I checked it, but when I changed a second outlet on the same breaker and the check that one with a 3-prong, 3-light checker it blow the middle light of the checker out and ungrounded the other circuit. Weird.
    Thanks for you help.
    There is definately something suspicious here.
    If you originally have 2 slot receptacle you wouldn't have a ground.
    What type of wiring do you have .... is it a cloth type covering on the 2 conductor cable or is is a flexable metal cover over the 2 conductors (BX) ?
    Is there a bare copper ground wire from the breaker panel to a ground rod or to the main water supply pipe where it enters to home?
    Are there series of wires running from the boxes to a water pipe running through the house?
    Jun 2008
    5
    It looks like I have both 2 cloth covered and flexable metal wires depending on the outler. The main breaker box has been replaced and is ground via a copper cable to the water main.
    That might explain why you were seeing an apparent ground on the plate screw on some outlets and not on others. The BX type metal case cable at some outlets would be showing the apparent ground and the cloth covered cables attached to the other outlets wouldn't show any ground.
    Did this also trip the breaker?
    Jun 2008
    5
    It didn't trip the breaker, just blew the middle light of the three-light tester.
    So were those boxes grounded or was it just a false reading?
    Quote Originally Posted by tmas View Post
    The testers typically use Neon bulbs ... can't say why it "blew" if it did.
    If those BX type cables run from the fixture box back to the service panel check the metal cable jacket for continuity to ground. There are likely metal cable strains that secure the cable to the metal service panel case and the fixture box for the receptacle. This would show the apparent ground at the receptacle .... this is an unreliable and inappropriate method to use as a grounding system for the receptacle.
    Sounds as though there is something strange going on and it may be in your best interest to have an electrician check things out ..... otherwise just guessing here.