    Default Re: Main Circuit Breaker Voltage Reading

    Good stuff .

  2. #22
    Join Date
    Jan 2008
    Posts
    27

    Default Re: Main Circuit Breaker Voltage Reading

    PROBLEM SOLVED!!! DJOHNS, Again thanks for your help. You hit it on the nose that it was a Power Company problem. I wasn't home when they came to fix it, and they didn't leave me an explanation as to what was wrong. I did however see that they replaced some connections. I am attaching a photo of the old connections I found laying on the ground and a picture of where they did the replacement with these little black boxes. Thanks to all who provided feedback.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	el1.jpg 
Views:	124 
Size:	16.7 KB 
ID:	864   Click image for larger version. 

Name:	el2.jpg 
Views:	128 
Size:	16.7 KB 
ID:	865  

  3. #23
    Join Date
    Aug 2007
    Location
    Denver, CO
    Posts
    666

    Default Re: Main Circuit Breaker Voltage Reading

    Interesting stuff.

    I have done many a service change and when we were finished I would tie the service conductors back into the utility drop with split bolt connectors. However that was not the end of it. After inspection I’d call the utility company with a closed loop request. They then would come out and replace my splices with high compression, insulated crimp sleeves and put a seal on the meter, leaving my split bolts on top of the meter for me to pick up later.

    Looks to me like the connectors in the right photo that they gunned off and left were never utility company connections…….. The tape job on them is atrocious.

    Kinda makes me wonder how that could have happened…….. Brother-in-Law Electric maybe?

  4. #24
    Join Date
    Aug 2007
    Location
    The deep South
    Posts
    459

    Default Re: Main Circuit Breaker Voltage Reading

    Thanks for the follow up report .

  5. #25
    Join Date
    Feb 2008
    Location
    west central new jersey
    Posts
    5

    Default Re: Main Circuit Breaker Voltage Reading

    Call the power company. It sounds like you have a loose connection (bug - a wire clamp) it is probibly at the connection just before it comes into your house. If it has been windy in your area and the lights flicker with the wind, it is a loose bug. Some power companies use aluminum wire from the pole to the house and copper in the pipe to the meter and breaker box. the wire clamps (bugs) get loose with time and as the aluminum wire corrodes. The lineman/trouble shooter will clean the connection and put some AL-CU compound on the wire put the bug back on and seal it.

  6. #26
    Join Date
    Jan 2008
    Location
    Lakeland ,MN
    Posts
    356

    Default Re: Main Circuit Breaker Voltage Reading

    Good call DJohns!!!!! You Da Man. My Dad Had the same thing happen to him. I talked him through it on the phone.

  7. #27
    Join Date
    Aug 2007
    Location
    The deep South
    Posts
    459

    Default Re: Main Circuit Breaker Voltage Reading

    Thank you , kind sir .