  1. #11
    Join Date
    Jan 2008
    Posts
    27

    Default Re: Main Circuit Breaker Voltage Reading

    What does PM stand for? I'm a newbie.

  2. #12
    Join Date
    Aug 2007
    Location
    The deep South
    Posts
    459

    Default Re: Main Circuit Breaker Voltage Reading

    private message

  3. #13
    Join Date
    Jun 2007
    Location
    Chicago, IL
    Posts
    162

    Default Re: Main Circuit Breaker Voltage Reading

    Your main breaker is fine. You have a bad connection somewhere between the utility pole & the main breaker. That is why you read full voltage under no-load (breaker off) but see a dramatic voltage drop under load (breaker on). Your utility company will probably check & repair/tighten connections at no charge to you, though if the bad connection has burned up anything in the meter socket, there may be a charge to repair it.
    HTH

    Dave

  4. #14
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: Main Circuit Breaker Voltage Reading

    I would have to agree with Dave..... though I wouldn't recommend inexperienced folks to open their electrical panels ... since you have different readings of 0V , 60V, 4V on that leg ... sounds like a problem between the feed outside from the utility to your panel.

    BTW...... Yuk Yuk where is that second picture from ?

  5. #15
    Join Date
    Aug 2007
    Location
    The deep South
    Posts
    459

    Default Re: Main Circuit Breaker Voltage Reading

    Canuk , check your mail .

  6. #16
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: Main Circuit Breaker Voltage Reading

    Quote Originally Posted by YukYuk View Post
    One of his other post strings from 01-23-08.

    http://advice.thisoldhouse.com/showt...2741#post12741

    Scary stuff.
    Just don't see how that has anything to do with this issue.

  7. #17
    Join Date
    Jun 2007
    Location
    Chicago, IL
    Posts
    162

    Default Re: Main Circuit Breaker Voltage Reading

    Quote Originally Posted by canuk View Post
    ..... though I wouldn't recommend inexperienced folks to open their electrical panels ...
    That's why I suggested calling the utility company. They'll come out for free, even on Sundays.
    HTH

    Dave

  8. #18
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: Main Circuit Breaker Voltage Reading

    Yep ... it's a nice thing to be able to get something free back from them.

  9. #19
    Join Date
    Jan 2008
    Posts
    27

    Default Re: Main Circuit Breaker Voltage Reading

    I appreciate all of your help. Especially you DJohns. I will now be waiting for the power company to come and diagnose a possible bad leg. I have managed to switched all of my essential power requirements(refrigerator, tv) to the good leg so I am ok for now. I will keep you all updated on the progress, and again thanks.

  10. #20
    Join Date
    Aug 2007
    Location
    The deep South
    Posts
    459

    Default Re: Main Circuit Breaker Voltage Reading

    Happy to help out . Hopefully the power company will get you back in business in short order .