    Just a few points
    1)almost all electronic filtering devices require a good ground to accomplish any filtering.

    2) most cheap UPS units only provide power when the power is off, the rest of the time the power supplied is directly from the incoming line. Better units(on-line UPS's) the power is supplied from the inverter at all times.

    3)The braided covering on the coaxial cable is a shield, if it is not properly grounded it becomes an antenna the picks up broadcasted signals from the air and outputs it as voltage.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  2. #62
    Join Date
    Sep 2013
    Location
    NM
    Posts
    2

    Default Re: voltage in cable coaxial

    Quote Originally Posted by JLMCDANIEL View Post
    If you have old outlets that are not keyed, that is both slots are the same size, you might try unplugging your TV, turn the plug over and plug it back in. And no an ungrounded GCFI outlet will not work.
    Jack
    For a fact, the only code approved way to replace a two wire ungrounded outlet with a three wire grounded outlet is to use a GFCI receptacle with a jumper between the neutral and the ground terminals on the device. In doing this, you have to affix a sticker which clearly states "This Is Not A Grounded Outlet," or words to that effect. This allows the use of three wire cords, and the GFCI will trip if the neutral is broken, but it does not magically provide a ground. While neutral and ground are essentially the same electrical point, they are two different ---but related--- things.

    This will not, however, fix the voltage on coax shield problem. That's a whole 'nother smoke.

  3. #63
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,901

    Default Re: voltage in cable coaxial

    Quote Originally Posted by EE98 View Post
    For a fact, the only code approved way to replace a two wire ungrounded outlet with a three wire grounded outlet is to use a GFCI receptacle with a jumper between the neutral and the ground terminals on the device. In doing this, you have to affix a sticker which clearly states "This Is Not A Grounded Outlet," or words to that effect. This allows the use of three wire cords, and the GFCI will trip if the neutral is broken, but it does not magically provide a ground. While neutral and ground are essentially the same electrical point, they are two different ---but related--- things.

    This will not, however, fix the voltage on coax shield problem. That's a whole 'nother smoke.
    Absolutely not correct. Jumpering the neutral and ground is called a "bootleg ground" and is NOT PERMITTED. Installing a GFI is an acceptable way of protecting an ungrounded circuit, and it and all downstream receptacles must be labeled as being ungrounded.

    If you jumper the ground and the neutral becomes broken upstream of the GFI, the ground will become live. "Grounded" appliances will have their chassis electrified which becomes a shock hazard. The GFI cannot protect against this shock hazard.

    Besides, you resurrected a thread that's over five years old with information that's irrelevant to the original post. That's classic behaviour of a spammer.
    Last edited by Fencepost; 09-10-2013 at 12:52 AM.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  4. #64
    Join Date
    Sep 2013
    Location
    NM
    Posts
    2

    Default Re: voltage in cable coaxial

    Print my post and your comment, and contact your local electrical inspector.

  5. #65
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,901

    Default Re: voltage in cable coaxial

    Article [250.24 (A)(5)] of the National Electrical Code reads thusly:

    "Neutral-to-Ground Connections. A neutral-to-ground connection shall not be made on the load side of the service disconnecting means except as permitted for separately derived systems [250.30(A)(1)], separate buildings or structures [250.32(B)(2)], or meter enclosures [250.142(B) Ex. 2]."

    Connecting the ground and neutral at a receptacle on a branch circuit (including GFI receptacles) is a violation of this code requirement. Ask your inspector how it isn't.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.