    Question 2 conductor woes

    Lots of electronic failures in old house with 2 conductor wiring!
    Do surge supressors not help on 2 conductor AC?
    Have lost display on microwave, a laser printer, an answering machine and a digital clock so far.
    Have a new service from the "pole" to the service head now,
    House is old with lath and plaster, so running new romex is a bit problematic...
    Ideas?

    thanks

  2. #2
    Join Date
    Jan 2008
    Posts
    2,091

    Default Re: 2 conductor woes

    Surge suppressors MUST be grounded to work properly; the ground conductor is where they send those surges to! Even with all the costs and trouble, you really should rewire the place if you plan on keeping it from turning into a pile of ashes. And you'll have to do this to sell it as most banks no longer make mortgage loans on houses with old or ungrounded wiring. Old wiring circuits were never intended to carry the loads we give wiring today; back then a few lights, a radio, and a toaster was about all they were expected to see at the same time(if that much). Add there being no GFCI's in damp locations with ancient fuseboxes and you're heading for disaster at high speed. Most homeowner's insurance will reduce their rates when you do an up-to-date by-code rewire which will offset the cost in time. I know it's not what you wanted to hear but it's what you really need to do.

    MC

  3. #3
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: 2 conductor woes

    Yep .. pretty much as MC stated.
    there may be some helpful information here or not : http://advice.thisoldhouse.com/showthread.php?t=1768

  4. #4
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,798

    Default Re: 2 conductor woes

    Besides the need for ground for surge suppressors almost all electronic equipment have some filtering built in which also require a good ground.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  5. #5
    Join Date
    Feb 2008
    Posts
    19

    Exclamation Re: 2 conductor woes

    Like all have stated. You need a ground for a surge suppressor to work. I suspect in your home you can use a cold water pipe or drive a grounding rod. Check your local codes. Running romex is your best method over the knob and tube. Just be sure to take out the old know and tube as you go. Or the two conductor. Look at the bright side of all when you finish this project of updating your electrical your home will have increased value. One word of caution permits are pretty resionable--Be sure to get one. You can keep the signed off permit to document the upgrades. Good luck and dig in. If you can't do this on your own always contact a professional.