    My standard 120V outlet suddenly went dead, kinda. C/B okay.

    My troubleshooting led me to this odd discovery. I pulled the recepticle out thereby leaving only bare wires to test with my voltmeter.

    2 black load, 2 white neutral, and ground are in the box. One of the black load wires will read a good solid 120v when I touch the voltmeter to the ground. Oddly, the same black load wire will read only 55-60v when I touch the voltmeter to either of the two neutral white wires.

    Subsequently, when the load and neutral are connected to the recepticle, the recepticle reads only 55-60v. What is going on?

  2. #2

    Default Re: Outlet Wiring Issue

    Check neutral at the breaker box.
    check neutral to ground.
    check across breaker

    are you in line with a gfi anywhere -check the kitchen, bath garage everone you can find -GFI's can have other outlets wired from them

  3. #3
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,062

    Default Re: Outlet Wiring Issue

    It sounds like you have an open neutral some where along the line and are reading through sanother device on the line.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  4. #4
    Join Date
    Aug 2007
    Posts
    612

    Default Re: Outlet Wiring Issue

    As was mentioned, you probably have a bad neutral connection. To narrow down where it is you need to start back tracking to the panel.