    Default steam radiator

    All radiators in my daughters old dutch colonial in eastern U.S. have been working fine except for one room. I checked the pipe in the basement leading to the second floor when heat is on and the pipe is hot. When I checked the pipe attached to the radiator the pipe is cold. It did work once last year but not since. Could it be air in the lines? If it was the shut off valve we would at least get hot pipes feeding the source.

    Do we have to change the pipes due to rust?

    Can I take the shut off valve off the radiator and run a small snake down to clear the pipe or would that cause rust particles to block some other area?

    Is there any additive that I cold put into the system to help this?

    Need help, fixitpa

  2. #2
    Join Date
    Nov 2009
    Posts
    71

    Default Re: steam radiator

    Try taking the vent off when the heat is on. That's the little "whistler" on the opposite side from where the valve is.

    If it heats up,replace that steam vent. If it still doesn't heat,

    You could have a blockage in that pipe or the valve is not really open. One other thing to check is that the radiator itself tilts back towards the valve a bit.Put a level on top of it and see whether it slopes towards the valve. If it slopes the other way, water can condense and cause the same symptom.

    No additives that I know of.
    Last edited by jpsmithny; 11-28-2009 at 08:38 PM.

  3. #3
    Join Date
    Nov 2009
    Posts
    2

    Default Re: steam radiator

    Thanks for the info. I just checked the pipe coming from the basement and it was hot. As I reached down through the 2nd floor, theres about 6" to 8 " between floor and 1st floor celiing and the pipe is cold. There is ample heat throughout the house except this one room. Your suggestions are good. I'll try them and let your know. Tks

    Any ideas of how to unplug the blockadge?

  4. #4
    Join Date
    Aug 2008
    Location
    Midwest
    Posts
    179

    Default Re: steam radiator

    Most of these problems are either the inlet shut off valve, the air vent, or the thermostatic trap on the outlet. In my experience, less than 10% of the problems with steam radiators were due to a blocked pipe, and never was it in a steam supply, just the condensate return, and never in a vertical section. Traps and air vents fail first, and hand valves second. It is a simple fix unless you break something.
    Last edited by ZZZ; 12-02-2009 at 09:13 PM. Reason: new & improved
    "Lead by Example"

  5. #5
    Join Date
    Aug 2008
    Location
    Midwest
    Posts
    179

    Default Re: steam radiator

    Why has GHIJ420 been allowed to post 18 spam messages since November 10 without getting banned from this site? And is he really stupid enough to think someone would buy clothes from a spam message on a home repair site? Yeah, that's the type of person I would want to do business with.
    "Lead by Example"

  6. #6
    Join Date
    Jul 2009
    Location
    Northeast
    Posts
    661

    Default Re: steam radiator

    Yesterday I went to the tools part of this site and didn't even hint about selling anything and a POP UP Message from the Moderator told me that my message would not be posted until it was reviewed, but all this other crap gets posted??? What is up with that????