    I replaced a switch in th bathroom of my 100 year old house and the wiring is insulated with, I believe cloth, I guess the typical old type of wiring. Anyway, the switch that I replaced did not have a ground wire and the new one does. Should I ground it to the box, even though I am not sure if the box itself if grounded? If not, should I put the old switch back in?

  2. #2
    Join Date
    Feb 2009
    Posts
    693

    Default Re: Ground - New switch old wiring

    The box is not grounded. It is fine to put the new switch in and not tie the ground to anything.

  3. #3
    Join Date
    Sep 2009
    Location
    jersey
    Posts
    174

    Default Re: Ground - New switch old wiring

    Quote Originally Posted by NEC View Post
    The box is not grounded. It is fine to put the new switch in and not tie the ground to anything.
    ??

    I dont disagree with NEC but I think he also wanted to say that you have to make sure the fixture is rated for use with no Equipment ground, usually meaning no exposed metal parts.

    I will add that no equipment ground is a pretty good indication that the wiring in your home is suspect to say the least and looking into it a little further would probably be a good idea.
    Help us name our new Hidden Content

  4. #4
    Join Date
    Feb 2009
    Posts
    693

    Default Re: Ground - New switch old wiring

    I think Lloyd may have been thinking about NEC article 404.9(B)

    "Exception to (B): Where no means exists within the snapswitch
    enclosure for connecting to the equipment grounding
    conductor or where the wiring method does not include
    or provide an equipment grounding conductor, a snap
    switch without a connection to an equipment grounding
    conductor shall be permitted for replacement purposes
    only. A snap switch wired under the provisions of this exception
    and located within reach of earth, grade, conducting
    floors, or other conducting surfaces shall be provided
    with a faceplate of nonconducting, noncombustible material
    or shall be protected by a ground-fault circuit
    interrupter."

    Note that the exception includes, "located within reach of earth, grade, conducting floors,or other conducting surfaces." and then the face plate or GFCI requirements if located therein. Notice also that if the switch is not located in an area mentioned above you can just replace it and are good to go.
    Last edited by NEC; 11-21-2009 at 06:10 AM.

  5. #5
    Join Date
    Sep 2009
    Location
    jersey
    Posts
    174

    Default Re: Ground - New switch old wiring

    Quote Originally Posted by NEC View Post
    I think Lloyd may have been thinking about NEC article 404.9(B)

    "Exception to (B): Where no means exists within the snapswitch
    enclosure for connecting to the equipment grounding
    conductor or where the wiring method does not include
    or provide an equipment grounding conductor, a snap
    switch without a connection to an equipment grounding
    conductor shall be permitted for replacement purposes
    only. A snap switch wired under the provisions of this exception
    and located within reach of earth, grade, conducting
    floors, or other conducting surfaces shall be provided
    with a faceplate of nonconducting, noncombustible material
    or shall be protected by a ground-fault circuit
    interrupter."

    Note that the exception includes, "located within reach of earth, grade, conducting floors,or other conducting surfaces." and then the face plate or GFCI requirements if located therein. Notice also that if the switch is not located in an area mentioned above you can just replace it and are good to go.
    I was refferring to the need to install a fixture rated for use without an equipment ground, ATM I dont have the article to reference however.
    Your point is noted but I wonder what "within reach" means
    48"CFF ? 54?

    Lets step awy from the NEC for a second and look at the purpose...
    To avoid having "unbonded" metal non current carrying parts being exposed. Put a plastic cover on the switch your probably ok, but installing a fixture with the same metals parts exposed and unbonded to an equipment ground would create the same potential hazzard 404.9 tries to avoid the plastic cover requirements. In fact theres probably more likely a chance for a short in a chandelier then a switch, hence more of a need to ground the metal parts.

    So, I think I'm agreeing just think its common to underestimate the importance of grounding fixtures.

    Example .. short in a fixture wire no egc .. bulb doesnt come on so homeowner goes to change it grabs the fixture... becomes the equipment ground... etc etc
    Help us name our new Hidden Content

  6. #6
    Join Date
    Feb 2009
    Posts
    693

    Default Re: Ground - New switch old wiring

    Quote Originally Posted by Lloyd View Post
    I was refferring to the need to install a fixture rated for use without an equipment ground, ATM I dont have the article to reference however.
    Your point is noted but I wonder what "within reach" means
    48"CFF ? 54?

    Lets step awy from the NEC for a second and look at the purpose...
    To avoid having "unbonded" metal non current carrying parts being exposed. Put a plastic cover on the switch your probably ok, but installing a fixture with the same metals parts exposed and unbonded to an equipment ground would create the same potential hazzard 404.9 tries to avoid the plastic cover requirements. In fact theres probably more likely a chance for a short in a chandelier then a switch, hence more of a need to ground the metal parts.

    So, I think I'm agreeing just think its common to underestimate the importance of grounding fixtures.

    Example .. short in a fixture wire no egc .. bulb doesnt come on so homeowner goes to change it grabs the fixture... becomes the equipment ground... etc etc
    "Jhust make shurr youh useh a fibba glass shtep ladda, Thape tha hends of the whias and ahll will be fhine."