    Default heater "fan only" operation

    I have a gas fired furnace in the pole barn of a house I just bought. The thermostat has a two wire lead running to it, with connections to "W" and "R". It functions properly in the heat/auto mode, but will not work in the fan only mode. Any idea how to make it work in fan only mode? Based on looking at the house thermostat, I'm guessing that I need another two wire lead to "G" and "Y" ---anyone know for sure.

  2. #2
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: heater "fan only" operation

    Yep ---- you need to run a wire from the " G " connection on the thermostat to the furnace " G " connection. This is for the fan manual operation.

    The " Y " is for air conditioning.


    Hopefully this helps.
    "" an ounce of perception -- a pound of obscure "
    - Rush

  3. #3
    Join Date
    Nov 2009
    Posts
    4

    Default Re: heater "fan only" operation

    Thanks, appreciate the help.