    Default 12 wire V. 14 wire for circuits

    This is what I get for over thinking again. I was all set to use 12 wire, 20 amp breakers, for the new circuits going to the bedrooms, however, i read that any lighting should be placed on 14 wire, 15 amp breaker, to limit the current passing through the filaments.

    Would it be better to run a single 15 amp circuit for the lighting then seperate 20amp circuits for the outlets? Or just 15 amp all around?

  2. #2
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,557

    Default Re: 12 wire V. 14 wire for circuits

    The size of the wire will not noticably limit the current going through a filament. Cost is usually the factor for using 14 instaed of 12.

    I like to have the lighting and the outlets on seperate cuircuits but it is not required.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  3. #3
    Join Date
    Feb 2009
    Posts
    693

    Default Re: 12 wire V. 14 wire for circuits

    [QUOTE=charleswaz;64246] however, i read that any lighting should be placed on 14 wire, 15 amp breaker, to limit the current passing through the filaments.
    QUOTE]

    Now in 30 + years in the electrical trade I've never heard that one!

    Jack offers good advice.

  4. #4
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,359

    Default Re: 12 wire V. 14 wire for circuits

    It won't limit the current going through the filament, unless there is noticeable voltage drop in comparison to using 12 gauge wire. The voltage drop would happen because of excessive distance (in which case you would be required to upsize the wire anyway) or continually running the circuit near capacity.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  5. #5
    Join Date
    Mar 2009
    Location
    wisconsin
    Posts
    159

    Default Re: 12 wire V. 14 wire for circuits

    some one filled ya with aline about more current running through it.. i persoanlly run as much 14 as i can to make it easy on myself making up devices.. and it is also a bit cheaper, but for me its the ease of it!! feel free to run 12 all day long to your lights thou..

  6. #6
    Join Date
    Sep 2009
    Location
    jersey
    Posts
    174

    Default Re: 12 wire V. 14 wire for circuits

    If you have 12 in allready dont change it. Its fine. The biggest disadvantage to using 12 over 14 is the way it eats up the wire fill in a givin box, and as someone else said a bit harder to make a termination on a device (requires a little extra squeeze to make sure its wrapped around the screw all the way) cost advantages and ease of pull fall toward 14 as well, but none of these make enough of difference to really matter in an attic.

    Does bring up a good point with wire fill tho, look inside those plastic boxes it will tell you how many individual conductors you can have per box. Dont forget to subtract 2 for each device, and all of your equipment grounds count as 1. Overfill is a pretty common fail around here. You can get quite a bit of 12 wire in those plastic round boxes you would typically be using for lighting, but the single gang plastic you are using for a switch is another issue, only allows you 9 -2 for device -1 for ground thats 6 or 3 12/2 so feed in feed out and switch leg, if its a 3 way you would have to drop the feed out and leave a feed in traveler and switch leg. Of course all depending on the size of the box your using.

    edited to add
    I hope we get some pics of all this at some point.
    Last edited by Lloyd; 10-15-2009 at 12:15 PM. Reason: added
    Help us name our new Hidden Content

  7. #7
    Join Date
    Jun 2007
    Location
    Shamokin, Pa.
    Posts
    645

    Default Re: 12 wire V. 14 wire for circuits

    [QUOTE=NEC;64252]
    Quote Originally Posted by charleswaz View Post
    however, i read that any lighting should be placed on 14 wire, 15 amp breaker, to limit the current passing through the filaments.
    QUOTE]

    Now in 30 + years in the electrical trade I've never heard that one!

    Jack offers good advice.