Page 2 of 2 FirstFirst 12
Results 11 to 12 of 12
  1. #11
    Sep 2009
    jersey
    174
    Default Re: Running Feeds into Main Service Panel
    Quote Originally Posted by christech View Post
    Lloyd,
    What does one check for on the cable clamp? Does the cable clamp specify the number of wires allowable through the clamp? Overall, is there a limit to the number of wires that I should run through the hole in a 200 AMP box? For example, if I run a 3 wire 12/3 and a 12/2 will I get flagged by the inspector? What's your experience?
    Thanks,
    Chris
    The best answer is sometimes. I have seen inspectors say you cant , you shouldn't, its fine etc etc. In my opinion using 12 wire you can have 5 current carrying #12 conductors through one 3/8" steel nm connector but only 3 or 4 with 14. and yes a nuetral is a "current carrying conductor" You would probably be ok with a 12/3 and 12/2 in the same connector. I have certainly seen much much worse. Probably even ok with a 14/2 and a 14/3 under the same one, 2 12/3 or 14/3 would be excessive. You could get the fill specs from the manufacturer, but its really not that big of an issue. The fact that your using a steel or cast connector over plastic is IMO a sign that your trying to use the best method. I really think you will be fine but if want some reasurance post the number and size of all the wires going in and the number and size of knock outs and we can get more specific.
    Help us name our new Hidden Content
  2. #12
    Shamokin, Pa.
    645
    Quote Originally Posted by Lloyd View Post
    I would agree with that, Lloyd. As usual the final say is with the inspector.
    Chris, have you though about stacking 2 12/2 cables per 3/8" Romex clamp and running the 12/3s in a Romex clamp by itself?