    Default Re: # of wires in PVC Conduit

    Quote Originally Posted by charleswaz View Post
    Thank you all for the replies. For clarification I am looking to run at least SIX 12/2(with ground) (yellow) romex lines up a straight shot from an unfinished basement through a vertical run with maybe one street elbow at the exit into the unfinished attic. One of the beauties of it being an old house (maybe the only beauty lol) is that the wall cavities are completely hollow so i can put as many conduits as necessary. I just didn't want to run into any issues as far as bundling too many lines together. I hope this makes it a little easier to help with
    Good luck with the project !!!!

  2. #12
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,622

    Default Re: # of wires in PVC Conduit

    Quote Originally Posted by NEC View Post
    If that is the case then I would forget about conduit and related derating issues. Drill a series of holes and do not bundle more than two cables through a hole.
    Quote Originally Posted by Lloyd View Post
    The conduit only complicates things, not only wire fill but firestopping. If your house is balloon framed I would skip it.
    Probably the best two pieces of advice.