    Default # of wires in PVC Conduit

    I am looking to run atleast 6 #12 wires up through a wall. I would like the ability to run additional lines later on down the road if needed so I am wondering what size PVC conduit I should use? Thanks for any help

  2. #2
    Join Date
    Feb 2009
    Posts
    693

    Default Re: # of wires in PVC Conduit

    Depends on how many wires and size You want to add and if too many derating becomes an issue.

    3/4" minimum.

  3. #3
    Join Date
    Jun 2007
    Location
    Shamokin, Pa.
    Posts
    645

    Default Re: # of wires in PVC Conduit

    It basically depends on the type of insulation and size of the conduit.
    For example.
    If you are using THHN, the most common in these parts, you can pull a count of 15 conductors [#12 AWG] though 3/4" rigid PVC Sched 40/ HDPE conduit, per the 2005 NEC, which I happen to have access to right now.
    If you have a specific type of conductor & conduit I will research the exact total allowed.

  4. #4
    Join Date
    Feb 2009
    Posts
    693

    Default Re: # of wires in PVC Conduit

    Quote Originally Posted by Ernie_Fergler View Post
    It basically depends on the type of insulation and size of the conduit.
    For example.
    If you are using THHN, the most common in these parts, you can pull a count of 15 conductors [#12 AWG] though 3/4" rigid PVC Sched 40/ HDPE conduit, per the 2005 NEC, which I happen to have access to right now.
    If you have a specific type of conductor & conduit I will research the exact total allowed.
    All well and good but do not forget about the derating part my friend.

  5. #5
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,359

    Default Re: # of wires in PVC Conduit

    Quote Originally Posted by charleswaz View Post
    I am looking to run atleast 6 #12 wires up through a wall. I would like the ability to run additional lines later on down the road if needed so I am wondering what size PVC conduit I should use? Thanks for any help
    Please clarify: do you mean 6 individual #12 wires (THHN) or do you mean 6 "Romex" cables, of size 12/2+ground (usually have a yellow jacket)?
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  6. #6
    Join Date
    Sep 2009
    Location
    Cleveland,Ohio/San Diego, California
    Posts
    18

    Default Re: # of wires in PVC Conduit

    charleswaz,

    In pvc conduct, a good rule of thumb is usually 3/4" (bigger the better). I would also consider running a second conduit for your future runs(containing no wires)if your budget allows for it.

    Some additional helpful tips for installing pvc electrical conduit-

    1. Try to align all your joints in the same direction. In other words, make sure that in the direction your pulling your wires try to minimize any internal lips that can hang up your wire or fish line.

    2. Use large radius sweeping elbows where you can.

    3. Dry fit all your work first before gluing.

    4. Use duct tape to cap the ends to avoid any contaminates from entering the conduit.

    Hope the tips help you out and good luck!


    Pete

    _______________________
    Measure once, Cut twice

  7. #7
    Join Date
    Jun 2007
    Location
    Shamokin, Pa.
    Posts
    645

    Default Re: # of wires in PVC Conduit

    Quote Originally Posted by Fencepost View Post
    Please clarify: do you mean 6 individual #12 wires (THHN) or do you mean 6 "Romex" cables, of size 12/2+ground (usually have a yellow jacket)?

    I too was wondering what exactly the OP was pulling.It just seemed to me like they were referring to spool wire, not Romex.
    On occasion we all will pull a run of Romex though PVC for protection.
    Without a doubt more info is paramount.

  8. #8
    Join Date
    Sep 2009
    Posts
    7

    Default Re: # of wires in PVC Conduit

    Thank you all for the replies. For clarification I am looking to run at least SIX 12/2(with ground) (yellow) romex lines up a straight shot from an unfinished basement through a vertical run with maybe one street elbow at the exit into the unfinished attic. One of the beauties of it being an old house (maybe the only beauty lol) is that the wall cavities are completely hollow so i can put as many conduits as necessary. I just didn't want to run into any issues as far as bundling too many lines together. I hope this makes it a little easier to help with

  9. #9
    Join Date
    Feb 2009
    Posts
    693

    Default Re: # of wires in PVC Conduit

    Quote Originally Posted by charleswaz View Post
    Thank you all for the replies. For clarification I am looking to run at least SIX 12/2(with ground) (yellow) romex lines up a straight shot from an unfinished basement through a vertical run with maybe one street elbow at the exit into the unfinished attic. One of the beauties of it being an old house (maybe the only beauty lol) is that the wall cavities are completely hollow so i can put as many conduits as necessary. I just didn't want to run into any issues as far as bundling too many lines together. I hope this makes it a little easier to help with
    If that is the case then I would forget about conduit and related derating issues. Drill a series of holes and do not bundle more than two cables through a hole.

  10. #10
    Join Date
    Sep 2009
    Location
    jersey
    Posts
    174

    Default Re: # of wires in PVC Conduit

    The conduit only complicates things, not only wire fill but firestopping. If your house is balloon framed I would skip it.