+ Reply to Thread
Results 1 to 3 of 3
Thread: Sizing the OCPD
  1. #1
    Join Date
    Aug 2007
    Unhappy Sizing the OCPD
    I need to do a service drop (single phase - 3 wire type XHHW - copper)cable.
    Because of a daily summer time temp of 113 (F) I need to factor the correction 0.82 into the calculation.
    Based on the math I did, I would need a 1350 kcmil copper cable (300 Amps) to feed 246 amps after the correction. 300 X 0.82 = 246 amps. Question, do I have to use a 300 Amp breaker or a 250 Amp breaker?
    Thanks in advance
  2. #2
    Join Date
    Mar 2009
    Default Re: Sizing the OCPD
    250 would be fine. you have to do all the correction factors to protect the wire, not the breaker
  3. #3
    Join Date
    Feb 2009
    113 F Temp? I am just laughing. Where do you live? Hell?