Results 1 to 10 of 10
    Jul 2009
    Default new panel for new home
    we are building a new home the plans say the eletrical VA quote is 55600 it says i need a 300 amp panel can anyone advise how you work this it ie how do you arrive at the figure 300amps from just 55600va
    Feb 2009
    693
    Default Re: new panel for new home
    Ohms law.
    55,600VA (Watts) / 240Volts = 231.666 Amps. Post back all electical usage and SQ/FT and would be happy to recalc.
    6,015
    Simple answer 55600va/240 volts =55600/240 volts = 231 amps
    If you actually have that much of a constant load you multiple the amps times 1.25 so 231 X 1.25= 288.75 amps The smallest panel avalible would then be a 300 amp panel and service.
    Feb 2009
    693
    Naw. Wrong.
    The first 10Kva is figured at 100% and the rest at 40% as far as service size per NEC.
    A load calc needs to be done for the home. Really doubt a 300A service is required.
    6,015
    Quote Originally Posted by NEC View Post
    Naw. Wrong.
    I said "If you actually have that much of a constant load " perhaps I wasn't clear enough, I guess I should have added "unlikely". But I do agree that a load calc needs to be done and doubt a 300 amp panel would be required.
    Feb 2009
    693
    If 55,600Va is a constant load, these folks need a serious lifestyle change.
    6,015
    Maybe they make a lot of money. Could be they are all plumbers.
    Feb 2009
    693
    Well, they are not electrical contractors for damn sure.
    Shamokin, Pa.
    645
    Just might be Al Gore's new cool abode.......
    6,015
    Perhaps a lot of grow lights?