Results 1 to 8 of 8
    May 2014
    Default Grounding to water meter
    I have a ground running from the electrical panel to the cold water pipe just before the meter. The ground wire does not jump the meter & my house has failed inspection.
    My questions are:
    Can I splice the existing wire with an additional piece to reach past the meter or do I have to replace the entire wire to reach past the meter?
    If so, is there a special connector that needs to be used to connect the wires?
    Jan 2011
    Columbiana, Alabama
    843
    Default Re: Grounding to water meter
    Quote Originally Posted by therealdusk View Post
    My questions are:
    There are special connectors and methods to extend the GEG (grounding electrode conductor) but they require a special crimper or mold to make them "irreverseable". So, if it's not too long a run from the electrical panel to the cold water pipe it may be easier to just run new #4 bare copper (#6 is OK if "not subject to physical damage).
    Be sure to use a waterpipe connector on the CW line within 5' of where it enters the house.
    Jun 2014
    6
    I think instead of paying excess money in buying connectors and other things you should replace complete wire.
    2,743
    Where I am, grounding to water lines is a no-go; the preferred method being dual ground rods outside as near to the meter as is practical. You'd already have the needed wire and those connectors are relatively cheap. Most electricians drive 'em in with a rotary hammer. Someone set up for this would be done in under 30 minutes and time is money! Check with the local inspector, but perhaps you can run a separate jumper from pipe to pipe across the meter, thus grounding your side of the system.
    we can't ground to the water line either
    6,077
    While metal water lines should be grounded, the proper way to ground the service is with prperly installed ground rods. The advent and use of PEX has made the water lines an unreliable ground source.
    Another vote not to use the CW pipe, even if your local code allows it.
    Jan 2011
    Columbiana, Alabama
    843
    Per 2014 NEC Art. 250.52
    Any of the following electrodes which are present in a structure must be bonded together to form a grounding electrode system:
    Metal underground water pipe (if at least 10 ft are buried outside) in addition, at least one other of the methods listed below must be used/installed
    Metal frame
    Concrete encased electrode
    Ground ring
    Ground rods (if present 2 are generally required)
    Plate electrodes
    Other local underground systems or metal structures
    Except: Aluminum electrodes or metal underground gas piping