+ Reply to Thread
Results 1 to 6 of 6
  1. #1
    Join Date
    Mar 2013
    Posts
    24

    Default taping into existing chain of outlets

    scenario #1
    if there is a direct linear chain of 5 residential outlet boxes is it acceptable to tap into one of the boxes in order to run another leg with another 1 or 2 duplex receptacles? if so is it acceptable to take off from the unused terminal screws of the outlet rather than have to redo the existing pigtails?

    scenario #2
    if there is no convenient existing outlet box to tap into is it acceptable to tap into the wire midway, add a splice/junction box and continue from there with the second leg?
    note- the only problem with this is that there is not enough slack in the wire so an additional foot of wire will be required to be spliced to extend to the existing run, meaning another splice box next to the junction box.

    thanks for the advice

  2. #2
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,047

    Default Re: taping into existing chain of outlets

    Scenario #1-Yes

    Scenario #2- Yes providing the new j-boxes are accessible.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  3. #3
    Join Date
    Jul 2010
    Location
    SoCal
    Posts
    7,762

    Default Re: taping into existing chain of outlets

    What Jack says, and let me add to #1: depending on what you will be running off these receptacles, is your breaker big enough?

  4. #4
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    843

    Default Re: taping into existing chain of outlets

    Ditto Jack and DJ.

    Also up to 13 receptacles or lights are allowed on a 20A circuit. Ten on a 15A.
    Good Luck from Columbiana, Alabama
    Maurice Turgeon, Hidden Content

  5. #5
    Join Date
    Mar 2013
    Posts
    24

    Default Re: taping into existing chain of outlets

    Thanks

    Is the 13 receptacle for a 20a circuit a hard line rule? Meaning one duplex outlet will count as two receptacles?
    The wiring in question will be for a basement workshop and i was going to use 4" sq boxes with two duplex outlets in each ( 2duplex=4 total outlets in each box)
    A lot of the devices will be low load items, lighting,chargers etc.

  6. #6
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,047

    Default Re: taping into existing chain of outlets

    A duplex receptacle is one receptacle.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •