    Default Should I replace all BX cable?

    Long story short, we have some 2-wire BX running meandering circuits in our house to the lights and a few outlets (like 3 in the whole house) with no rhyme or reason. Should I make it a priority to replace the BX?

    We replaced it in the 2 rooms we gutted, and when giving a room outlets I run a new cable and even try to move existing outlets from the BX to that new run, but should I try to rip it out other places like the lights? Or is it fine as is?

    (Note: it is a post and beam house, crumbly horse hair plaster, no attic, and the base board is pinned down by two thick layers of wood flooring and gargantuan cut nails. Almost every project is a mini nightmare.)

    I thought about putting a few of the lights on the outlet circuit, but I recall hearing that is bad form. Yet running a second circuit for just 1 or 2 light bulbs seems wasteful.

  2. #2
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,608

    Default Re: Should I replace all BX cable?

    Quote Originally Posted by skintigh View Post
    Long story short, we have some 2-wire BX running meandering circuits in our house to the lights and a few outlets (like 3 in the whole house) with no rhyme or reason. Should I make it a priority to replace the BX?
    It depends. How is the insulation? If it's brittle, you should make replacement a priority. Also, if you need to connect grounded devices, those circuits should be replaced. Any circuits to bathrooms or kitchens should be replaced and protected with GFIs. For those circuits that you aren't replacing yet, you could install AFI breakers, which may provide additional protection against fires started by arcing. Since bedroom circuits are now required to have AFI, it won't be wasted money. Probably other circuits, too, but I'm not fluent in the code.

    I thought about putting a few of the lights on the outlet circuit, but I recall hearing that is bad form. Yet running a second circuit for just 1 or 2 light bulbs seems wasteful.
    Bad form, but not prohibited. If you can wire them so they are on a different circuit from the receptacles in the same room, you can achieve the goal of not being totally without a light source in the room when a breaker trips. Make sure that the wiring to the light is rated for the ampacity of the circuit. If the breaker is 20A, you'll need 12AWG wire, even though the lamp will never draw more than a few amps.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  3. #3
    Join Date
    Oct 2012
    Location
    Houston, TX
    Posts
    295

    Default Re: Should I replace all BX cable?

    I know you said it is 2-wire, but is the grounding intact from the armor? If yes, and the wire isn't brittle as mentioned by Fencepost, don't make it too high a priority, do it when it is convenient as that wire is likely still safe.
    It's this old house, not this built after your dad was born house.

  4. #4
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,608

    Default Re: Should I replace all BX cable?

    Quote Originally Posted by function View Post
    I know you said it is 2-wire, but is the grounding intact from the armor? If yes, and the wire isn't brittle as mentioned by Fencepost, don't make it too high a priority, do it when it is convenient as that wire is likely still safe.
    To clarify, there are really three types to consider:
    • "BX" -- ("Product B - Experimental") -- Original product. Paper liner/wrap; does not have a bonding strip
    • AC -- ("Armored Cable") -- Replacement for "BX". Paper liner/wrap; has a bonding strip; jacket may be used as grounding conductor
    • MC -- ("Metal Clad") -- plastic liner; no bonding strip; insulated grounding conductor; jacket may NOT be used as a grounding conductor


    Actual "BX" contains no ground conductor besides the jacket itself. If the jacket rusts where it is clamped to a box, that can represent a high-resistance connection. Therefore, the jacket shouldn't be trusted as a grounding conductor. AC, the replacement for "BX", contains a bonding strip between the jacket and the liner; that is intended to allow the jacket to be used as a grounding conductor.

    Note that "BX" isn't an actual type defined by the NEC, but rather is a manufacturer's product designation. The only major types defined by the NEC are AC and MC. (I think. "BX" might have reference in the NEC, but without a valid grounding conductor it wouldn't be permitted for new install.)

    There are other differences between AC and MC, including where they may be used and how they are to be installed. But that's too much minutiae for discussion here.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  5. #5
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,798

    Default Re: Should I replace all BX cable?

    fencepost, your description of BX cable is completely different than what is called BX around here, and that is still avalible.



    Jack
    Last edited by JLMCDANIEL; 04-29-2014 at 03:52 PM.
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  6. #6
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,608

    Default Re: Should I replace all BX cable?

    Quote Originally Posted by JLMCDANIEL View Post
    fencepost, your description of BX cable is completely different than what is called BX around here, and that is still avalible.
    Is it actually labeled "BX" by the manufacturer? Or is that just what "everybody" calls it? Just because everybody calls it that doesn't mean that's what it is. My understanding is that it was originally a trademark, but has become genericized through popular use. "BX" is not a recognized type code by the NEC. AC and MC are recognized type codes.

    From the article at http://seatekco.com/bx-cable/ --
    "Today's armored cable, historically known as BX and more correctly as Type AC..."

    Not every facial tissue is Kleenex.
    Last edited by Fencepost; 04-29-2014 at 07:59 PM.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  7. #7
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,798

    Default Re: Should I replace all BX cable?

    From your article "Basic armored cable was developed in the early 1900s by Edwin Greenfield and Gus Johnson, who called their product BX cable. It has become a generic term for all armored cable." There is no mention in the OP that suggessts it is wiring from the early 1900's.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  8. #8
    Join Date
    Feb 2013
    Location
    Boston area
    Posts
    97

    Default Re: Should I replace all BX cable?

    Thanks for the help! Here are the details I left out:

    We gutted the kitchen and master bath so those rooms will be completely up to code. The other bathroom looks like it was remodeled in the 80s or later so electrically anyway it seems to be up to code and has a GFCI outlet (though the pipes are not pitched right and the town has no record of permits being pulled between 1865 and 2013...)

    The "BX" cable is 2 wire, and I don't see a paper liner or liner of any sort. The wires are white and black, with the black neutral and the white hot, at least in the ones I tested. The insulation seems to be a woven cloth over rubber, and is so old and dirty it's hard to tell white from black. It is crumbly at the ends but other than that seems to be in good shape. The connections are twisted and then coated in tar or some nasty black crap.

    Indoors it does not appear to have any rust. I used the shield as a ground for a few outlets just to get some 3-prongs and it seems to be working, my little tester was happy anyway. (I think only one of those is being used anymore but it's being used for my computer...) However, they also ran a bx line underground to the garage and it has rusted pretty much through. I think it is still powered, but I decided not to screw with it until I'm sure it is disconnected from the panel.

    The whole house is a hodgepodge. The master bedroom had 2 outlets on 2 circuits, one 3-prong and one 2-prong. Most rooms had either one 2-prong or no outlets at all. I was lazy and just turned off the hall light to work on it and got a shock on the neutral line, which was apparently tied to the master bedroom light which was on. Is that bad? Oh, and I think that one circuit went from the dining room outlet to living outlet the upstairs to a master outlet then to living light to master light to hall light to ??? So if we used the microwave and a heater or AC upstairs we would trip a breaker.

  9. #9
    Join Date
    Aug 2007
    Location
    Maryland
    Posts
    1,587

    Default Re: Should I replace all BX cable?

    I'll let more knowledgeable people comment about your issues, but I never work on electric unless the breaker is off and I test it to be sure. Thanks for the reminder why.

  10. #10
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    710

    Default Re: Should I replace all BX cable?

    Since you're already replacing a bunch now why not replace the BX before you start making the place pretty and it fails?

    IMO, there is no reason to spend a lot of time and money running separate light and receptacle circuits. It's not a Code issue.
    How often does one trip a breaker?

    I run all new circuits with #12 and mix lights & receptacles up, whatever is easiest. The big cost today is the AFCI breaker needed for most circuits.

    I also put freezers/refrigerators in a basement on a GFCI with a lighting circuit which will be noticed, if the GFCI breaker/receptacle trips.
    Good Luck from Columbiana, Alabama