    Quote Originally Posted by MtMan54 View Post
    Hi, If you are going to rewire then I would use #10 wire to keep your electric bill lower, forget about the #14 and #12 wire. Thanks
    I don't know what you're smoking, but it's certainly not #12 or #14 wires unless you're trying to run 30A loads on them.

    Wires don't consume electricity; they transmit it. A larger wire isn't going to be any more energy efficient than a wire that is properly sized for the load. The size of the wire isn't going to change your electric bill any more than reducing the number of outlets installed in your home.

    What a larger wire will be is more expensive and harder to work with. For fixed lighting circuits, you can use #14 wires and limit the load to about 12A (even though the circuit is rated for 15A, the NEC requires a continuous load not exceed 80% of the circuit rating). Except for kitchens & bathrooms, receptacle circuits may be wired with #14 (on a 15A breaker) though #12 (with a 20A breaker) is a good idea.

    Having light fixtures on separate circuits from receptacle outlets is a very, very good idea. That way, when a breaker trips, you'll still be able to have light in the room whether from the fixture or a portable lamp.

    There is no point in running oversized wire unless the circuit is an excessively long run (~100 feet; there are voltage drop calculations you can do but that's beyond the scope of this discussion). You're not allowed install 15A or 20A receptacles on a 30A circuit anyway.
    Last edited by Fencepost; 04-09-2014 at 02:56 PM.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  2. #12
    Join Date
    Apr 2014
    Posts
    17

    Default Re: Rewire Entire House

    Great reply above, I was thinking how can bigger wire save money! In fact I have heard using bigger wire that is not properly rated for the load you are putting on it, can have negative effects and 'draw' more causing heat? or other issues. Meaning if you are putting a load that could easily run on a 12 or 14/2 wire on a 10, might cause more draw etc. Again I am not an expert.

    Anyways here are my questions.

    How do you determine to run 12 or 14/2 in the house? I need to re-wire my entire house as well. I know for kitchen where there will be toasters, water kettles, and more running appliances you wold want to probably use 12/2 between 2, 20 amp circuits??

    Other general question

    I like the idea of having all the lighting on one circuit and outlets on another.

    so I know you can't exceed 80% of total circuit load. So If I take 2 bedrooms, each running a computer (700 Watt PSU /120 = 5.8 Amps), clock radio maybe a few other electronics but nothing out of normal besides the higher wattage computers, maybe another laptop running at 90Watts = .75 Amp, alarm clocks .041 amps, misc stuff etc... I shouldn't have more than 12 amps consumed at any given time. That fits under the 80% continuous load code. Would I be fine using 1, 15 Amp circuit running both of those rooms for the outlets? I would imaging I could run at least 3 rooms on another 15 amp circuit for the lighting. (3 rooms no more than 100 watt lighting) - I could probably run 4 rooms?

    Any thoughts here on this?

  3. #13
    Join Date
    Jan 2014
    Location
    NH
    Posts
    137

    Default Re: Rewire Entire House

    Quote Originally Posted by pcride View Post
    Great reply above, I was thinking how can bigger wire save money! In fact I have heard using bigger wire that is not properly rated for the load you are putting on it, can have negative effects and 'draw' more causing heat? or other issues. Meaning if you are putting a load that could easily run on a 12 or 14/2 wire on a 10, might cause more draw etc. Again I am not an expert.

    Anyways here are my questions.

    How do you determine to run 12 or 14/2 in the house? I need to re-wire my entire house as well. I know for kitchen where there will be toasters, water kettles, and more running appliances you wold want to probably use 12/2 between 2, 20 amp circuits??

    Other general question

    I like the idea of having all the lighting on one circuit and outlets on another.

    so I know you can't exceed 80% of total circuit load. So If I take 2 bedrooms, each running a computer (700 Watt PSU /120 = 5.8 Amps), clock radio maybe a few other electronics but nothing out of normal besides the higher wattage computers, maybe another laptop running at 90Watts = .75 Amp, alarm clocks .041 amps, misc stuff etc... I shouldn't have more than 12 amps consumed at any given time. That fits under the 80% continuous load code. Would I be fine using 1, 15 Amp circuit running both of those rooms for the outlets? I would imaging I could run at least 3 rooms on another 15 amp circuit for the lighting. (3 rooms no more than 100 watt lighting) - I could probably run 4 rooms?

    Any thoughts here on this?
    Hi, Just because you use #10 wire doesn't mean you have to use a 30amp breaker and a larger wire doesn't draw more and cause heat, it is just the opposite, using a smaller wire will draw more and cause heat. Thanks

  4. #14
    Join Date
    Feb 2013
    Location
    Boston area
    Posts
    112

    Default Re: Rewire Entire House

    He's right in that there would be less resistance and heat, but let's do some math as to how much...

    According to wikipedia:

    # Ω/kft
    10 0.9989
    12 1.588
    14 2.525

    So, 100 feet of #14 would have 0.15 ohms more resistance than #10, 100 feet of #12 would have less than 0.06 more ohms of resistance.

    0.15 ohms at 15 amps is 33.75W, compared to the ~1800W being used at 15A, or 1.875%.
    0.06 ohms at 20 amps is 24W, compared to the ~2400W being used, or 1%.
    (Did I do that part right? I was expecting smaller percentages.)

    Assuming I did that right, that means if I use all #10 I can save around 1.5%. So, if I spend $800 a year I will save $12/yr.

    Now, what is the added cost in materials and labor? 10/2 seems to cost $50 more per 100ft than #12 and $65 more than #14, but it might be cheaper in bulk. I imagine in addition to being more expensive and harder to snake, wiring outlets would be slower too as you can't fit #10 in the back of those little quick-connects (but I don't know if real electricians use those).

    I need to stop wasting time.

  5. #15
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,075

    Default Re: Rewire Entire House

    Quote Originally Posted by skintigh View Post
    He's right in that there would be less resistance and heat, but let's do some math as to how much...

    According to wikipedia:

    # Ω/kft
    10 0.9989
    12 1.588
    14 2.525

    So, 100 feet of #14 would have 0.15 ohms more resistance than #10, 100 feet of #12 would have less than 0.06 more ohms of resistance.

    0.15 ohms at 15 amps is 33.75W, compared to the ~1800W being used at 15A, or 1.875%.
    0.06 ohms at 20 amps is 24W, compared to the ~2400W being used, or 1%.
    (Did I do that part right? I was expecting smaller percentages.)

    Assuming I did that right, that means if I use all #10 I can save around 1.5%. So, if I spend $800 a year I will save $12/yr.

    Now, what is the added cost in materials and labor? 10/2 seems to cost $50 more per 100ft than #12 and $65 more than #14, but it might be cheaper in bulk. I imagine in addition to being more expensive and harder to snake, wiring outlets would be slower too as you can't fit #10 in the back of those little quick-connects (but I don't know if real electricians use those).

    I need to stop wasting time.
    First, the calculation you used is based on DC current resistance not impedance in AC wiring.
    Second, seldom is a circuit load at 80% full capacity let alone full capacity normally reached.
    Third, any good electrician will tell you not to use the stab connections in the back of the receptacle.
    Fourth, the code size rating already has a significant safety margin built in, going to #10 will only add to the cost and make installation many times harder.

    Most common practice is to use all 12 gauge cables because it is cheaper to buy in bulk one size cabling.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  6. #16
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    843

    Default Re: Rewire Entire House

    Quote Originally Posted by MtMan54 View Post
    Hi, If this was not important, then I would not say anything. Thanks
    While #10 wire would save energy lost because of long runs it would:

    1) very easily create "box fill" Code violations using standard boxes

    2) probably necessitate all connections to switches and receptacles to be "pigtailed" with stranded wire so they could be inserted into a box, without breaking the terminals off of the devices.

    3) very easily double the cost of labor and material for branch circuit wiring

    4) not allow the branch circuits to be protected with a breaker larger than 20A or have more than 13 outlets (receptacles or lights) on the circuit.

    5) take decades to break even, compared to using #12 or #14 wire.
    Good Luck from Columbiana, Alabama
    Maurice Turgeon, Hidden Content

  7. #17
    Join Date
    Jan 2014
    Location
    NH
    Posts
    137

    Default Re: Rewire Entire House

    Hi, There is one thing that people do today and that is they double or triple the number of outlets on a circuit with these power strips. Thanks

  8. #18
    Join Date
    Feb 2013
    Location
    Boston area
    Posts
    112

    Default Re: Rewire Entire House

    Quote Originally Posted by JLMCDANIEL View Post
    First, the calculation you used is based on DC current resistance not impedance in AC wiring.
    Second, seldom is a circuit load at 80% full capacity let alone full capacity normally reached.
    Third, any good electrician will tell you not to use the stab connections in the back of the receptacle.
    Fourth, the code size rating already has a significant safety margin built in, going to #10 will only add to the cost and make installation many times harder.

    Most common practice is to use all 12 gauge cables because it is cheaper to buy in bulk one size cabling.

    Jack
    1) You're right, that would change the impedance to 3.1, 2.0 and 1.2. Roughly the same ratio but I don't feel like redoing the math.

    2) Obviously, but the ratios are the same for any length or use. I just picked 100 feet at random and full current as I don't know what a typical use or run would be. What would be better? 20 feet and 25% load? If someone has real numbers maybe I'll make a spreadsheet.

    3) I have heard that, do they work loose?

    4) I think I already showed that's not entirely true -- it would save a tiny amount of money. I'm just wondering how that compares to additional costs.

    Maurice: if it doubles the costs like you are suggesting, I think your estimates on payback are low. Assuming wiring a house will cost in the 4-5 digit range, while yearly savings are in the 1-2 digit range, then payoff may take a millennium...

  9. #19
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,075

    Default Re: Rewire Entire House

    Quote Originally Posted by skintigh View Post
    1) You're right, that would change the impedance to 3.1, 2.0 and 1.2. Roughly the same ratio but I don't feel like redoing the math.
    Cute but no cigar, impedance calculations require much more than length and resistance. Code wiring has a greater than 50% load rating safety margin based on a wide temperature range.
    2) Obviously, but the ratios are the same for any length or use. I just picked 100 feet at random and full current as I don't know what a typical use or run would be. What would be better? 20 feet and 25% load? If someone has real numbers maybe I'll make a spreadsheet.
    The calculations have already be done in establishing the cabling needed to meet code. 12/2 costs are half of what 10/2 costs, so that double the installation material cost. Because of the extra labor required (making pig tails to connect devices, adding extra boxes to meet fill requirements, and harder to pull) that increases the installation cost.
    3) I have heard that, do they work loose?
    Over time due to vibration and heat they loose proper contact.
    4) I think I already showed that's not entirely true -- it would save a tiny amount of money. I'm just wondering how that compares to additional costs.
    If you spend 3600/yr on electric and can save 1.5% (if possible) you would save $54/yr, with installation and material cost cost of the 10/2 adding $10,000 to the cost the pay back would take 185 years.
    Maurice: if it doubles the costs like you are suggesting, I think your estimates on payback are low. Assuming wiring a house will cost in the 4-5 digit range, while yearly savings are in the 1-2 digit range, then payoff may take a millennium...
    See number 4 above
    I hope this helps you understand a little better.