Results 1 to 8 of 8
    Jan 2014
    Default Thermostat reading 10 degrees too high - wiring issue?
    Recently purchased a "fixer upper" and the thermostat was dirty and falling off the wall. I decided to replace it with a Honeywell programmable. The old thermostat had wires for Rc, Rh, W, Y, and G. I put the new Honeywell on with exactly the same connections, and the thermostat reads about 10 degrees higher than actual temperature in the room.
    I checked for dirt blocking the sensor, didn't find any, so I decided to replace the thermostat with a fancy NEST wifi thermostat. Contacted NEST to see if it would work with the Rc, Rh, W, Y, and G wires, and they said yes.
    Put the NEST on exactly as they recommended, but the NEST is reading the same way, about 10 degrees too high. I removed the thermostat from the base to make sure I wired it correctly, and noticed the spot where the Y wire is connected is extremely warm.
    I followed the thermostat wires down to where they connect to my furnace/AC, and saw that there are terminals marked Y, W, G, R, and C.
    I noticed the Y and W wires from the thermostat are both connected to the Y terminal on the transformer. The W terminal on the transformer is not connected to anything.
    The G wire on the thermostat is connected to the G terminal.
    The Rc wire from the thermostat is connected to the C terminal. The Rh wire is connected to the R terminal.
    Is having both Y and W connected to the Y terminal on the transformer be the source of my problem? Should I move the W wire over to the W terminal, or will that mess something up?
    1,002
    Default Re: Thermostat reading 10 degrees too high - wiring issue?
    is the thermostat located over a heater? is it located on a wall that has a heating pipe running up through the wall right behind it? what's on the other side of the wall that the thermostat is on? a piece of heat? an oven?
    2,737
    The way to verify a thermostat's accuracy is to put a known accurate thermometer right next to it where it will encounter the exact same conditions the thermostat does. Even the cheapest thermostat will usually be within a couple degrees unless something is wrong with it. If you're measuring anywhere else, then of course you're going to have a variation, just the same as measuring at the ceiling and floor levels brings different numbers.
    So what does a thermometer do to keep you comfortable? Nothing. So forget what the thermostat is set at- it means nothing- just make the house comfy and note what it says, then worry about undue variations from that number. And like MLB says, it's location matters so if it's poorly sited, move it.
    Jan 2014
    Thermostat is not over a heater or anything. It is on a wall where a duct from the furnace leads up to the second floor, but the thermostat reads high even when the heat is not running. I compared the reading with a thermometer next to it.
    Nobody thinks the wiring maybe an issue? Even when the base of the thermostat was extremely hot to the touch near the Y wire?
    Maryland
    2,009
    I'm going to say something is obviously wrong if the thermostat is extremely hot. Could be a fire hazard. I would say it's time to get an HVAC tech in to figure it out.
    Quote Originally Posted by ed21 View Post
    Yes, call a tech. You may have your wires messed up.
    2,737
    Thermostats should not 'heat up' except for the ones directly controlling electric baseboard heat- and even those rheostats shouldn't warm up much.
    My guess is that either the thermostat is mis-wired or that someone has replaced the low-voltage transformer in the furnace which supplies thermostat power with one running at a higher voltage during a repair. With it 'self-heating' something is definitely wrong and it will definitely be reading incorrectly!
    Dec 2013
    New Hampshire
    27
    Heat uses only the W and Rh terminals. Rc Y and G are used for air conditioning and fan-only settings. A warm wire to the Y terminal indicates a malfunction of the air conditioning circuit. Disconnect the wire to the Y, Rc, and G terminal and check the voltage of the transformer. High voltage may have caused a short in the thermostat and relay. The wires from the Rh and Rc should be connected to the transformer not the Y and W wires, but this reversal would only make the fan control inoperative.