    I am helping my daughter and son-in-law build their own house and we are doing the rough in plumbing. The house is 1600 sq ft on a crawl space. It has 2 full baths, washing machine, kitchen sink and a dishwasher. I am running a 4 inch waste line but I am not sure what size vent to run up through the roof. Sure would appreciate any help !

  2. #2
    Join Date
    Jul 2010
    Location
    SoCal
    Posts
    6,323

    Default Re: roughin plumbing

    3" for the kitchen, 2" for each bathroom, 2" for the washing machine. Large vents (7" or 8") for the gas range, 3" for the gas water heater.

    Not sure? call your building department. Or ask your friendly building inspector. Smile.

  3. #3
    Join Date
    Dec 2010
    Location
    Houston Texas
    Posts
    2,919

    Default Re: roughin plumbing

    Some vents can be tied together all into one vent, depending on the local codes. You'll need to check on that.

  4. #4
    Join Date
    Oct 2013
    Posts
    3

    Post Re: roughin plumbing

    Quote Originally Posted by pilgrimtj View Post
    I am helping my daughter and son-in-law build their own house and we are doing the rough in plumbing. The house is 1600 sq ft on a crawl space. It has 2 full baths, washing machine, kitchen sink and a dishwasher. I am running a 4 inch waste line but I am not sure what size vent to run up through the roof. Sure would appreciate any help !
    The size is usually governed by one of two different plumbing codes, the International Residential Code or the Uniform Plumbing Code. (Check with your local building department to see which code you should use).

    In the IRC, the code section is P3113.1 which requires the vent is to be 1/2 the size of the drain served (i.e. 2-inch for a 4-inch drain). Vents which exceed 40 ft. in developed length to be increased on size larger. So you could run a 2-inch diameter vent up to within 12-inches of the roof, where you may need to increase it to 3-inches for frost closure protection, if the winter design temperature in your area is 0 F or less. Terminate at least 6-inches above above the roof or 6-inches above the anticipated snow accumulation (whichever is greater).

    In the UPC, Section 904.1 also requires the vent to be not less than 1/2 the drain size and and sized to the total number of fixture units connected. Based on what you stated was connected, we can assume you have 17 fixture units. Table 7-5 allows 24 fu for a 2-inch vent so that would be the minimum acceptable. The UPC allows 2-inch pipe to terminate outside with a winter design temp of 0 F, but required you extend a minimum of 10-inches above the roof (or more if req by the AHJ).

    In either case, keep the vent termination at lease 10-feet from, or not less than 3-feet above, any window or air intake.

  5. #5
    Join Date
    Oct 2013
    Posts
    4

    Default Re: roughin plumbing

    Quote Originally Posted by dj1 View Post
    3" for the kitchen, 2" for each bathroom, 2" for the washing machine. Large vents (7" or 8") for the gas range, 3" for the gas water heater.

    Not sure? call your building department. Or ask your friendly building inspector. Smile.
    thank you...

  6. #6
    Join Date
    Oct 2013
    Posts
    4

    Default Re: roughin plumbing

    Quote Originally Posted by HoustonRemodeler View Post
    Some vents can be tied together all into one vent, depending on the local codes. You'll need to check on that.
    thank you....

  7. #7
    Join Date
    Oct 2013
    Posts
    4

    Default Re: roughin plumbing

    Quote Originally Posted by enigma-2 View Post
    The size is usually governed by one of two different plumbing codes, the International Residential Code or the Uniform Plumbing Code. (Check with your local building department to see which code you should use).

    In the IRC, the code section is P3113.1 which requires the vent is to be 1/2 the size of the drain served (i.e. 2-inch for a 4-inch drain). Vents which exceed 40 ft. in developed length to be increased on size larger. So you could run a 2-inch diameter vent up to within 12-inches of the roof, where you may need to increase it to 3-inches for frost closure protection, if the winter design temperature in your area is 0 F or less. Terminate at least 6-inches above above the roof or 6-inches above the anticipated snow accumulation (whichever is greater).

    In the UPC, Section 904.1 also requires the vent to be not less than 1/2 the drain size and and sized to the total number of fixture units connected. Based on what you stated was connected, we can assume you have 17 fixture units. Table 7-5 allows 24 fu for a 2-inch vent so that would be the minimum acceptable. The UPC allows 2-inch pipe to terminate outside with a winter design temp of 0 F, but required you extend a minimum of 10-inches above the roof (or more if req by the AHJ).

    In either case, keep the vent termination at lease 10-feet from, or not less than 3-feet above, any window or air intake.

    appreciate that.....you were a big help.