    Default Re: Weird shared nuetral w/ double breaker

    Quote Originally Posted by The Semi-Retired Electric View Post
    Breakers with handle ties are not 2 pole circuit breakers. 2 pole (and 3pole) circuit breakers are manufactured with internal common trip unless otherwise labeled. You are correct that MWBC's can use handle ties or multi-pole breakers.
    Granted a small percentage of double or three pole breakers have only one trip handle.
    But, most have a handle for each "phase" and employ internal trip and the handles handles are always tied together.

    The internal trip ensures all the "phases" will open together but the tie handle may allow a "phase" remain closed.

    I don't understand what you mean "Breakers with handle ties are not 2 pole circuit breakers".[/QUOTE]

    I meant two single pole circuit breakers, adjacent to one another, joined by handle ties may be used for MWBC's.

  2. #12
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    623

    Default Re: Weird shared nuetral w/ double breaker

    Quote Originally Posted by brrichter View Post
    Granted a small percentage of double or three pole breakers have only one trip handle.
    But, most have a handle for each "phase" and employ internal trip and the handles handles are always tied together.

    The internal trip ensures all the "phases" will open together but the tie handle may allow a "phase" remain closed.

    I don't understand what you mean "Breakers with handle ties are not 2 pole circuit breakers".
    I meant two single pole circuit breakers, adjacent to one another, joined by handle ties may be used for MWBC's.[/QUOTE]

    Sounds like we were both saying the same thing

    Also, it appears the OP solved his problem..life is good.
    Good Luck from Columbiana, Alabama
    Maurice Turgeon, Hidden Content

  3. #13
    Join Date
    Sep 2013
    Posts
    4

    Default Re: Weird shared nuetral w/ double breaker

    Quote Originally Posted by The Semi-Retired Electric View Post

    Also, it appears the OP solved his problem..life is good.
    Indeed, indeed.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •