+ Reply to Thread
Results 1 to 5 of 5
  1. #1
    Join Date
    Jun 2010
    Posts
    43

    Default Hanging light fixture above a tub?

    We're preparing to remodel our master bath. The tub is centered under a window in an alcove. Currently, there is a pot light centered in the ceiling above the tub. I got a strange look from one contractor when mentioning I'd like to replace the pot light with a hanging fixture (chandelier). Another contractor told me it would be against code to have a chandelier hanging above a tub. However, I've seen tons of home remodeling shows on TV where the contractor installs such a hanging fixture above a tub. So, what gives?

  2. #2
    Join Date
    Sep 2012
    Location
    Boston
    Posts
    1,002

    Default Re: Hanging light fixture above a tub?

    we installed one once two years ago, same situation, on a large bathroom remodel done on a permit. electrical inspector saw it during final inspection, signed off on it and never mentioned it other than saying "w-o-w, that looks nice". i would call the electrical inspector in your town and ask. it might be different in each state or town.

  3. #3
    Join Date
    Dec 2010
    Location
    Houston Texas
    Posts
    3,179

    Default Re: Hanging light fixture above a tub?

    The location makes dusting the light fixture a tad tricky.

    Do check with the inspector first.

  4. #4
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,890

    Default Re: Hanging light fixture above a tub?

    As long as the bottom of the chandelier is 8 feet above the rim of the tub, you're OK. Otherwise, you must use a fixed-in-place (not a pendant) fixture that is listed as suitable for damp locations.

    I found a reference to the 2005 National Electrical Code:

    Article 410

    Luminaires (Lighting Fixtures), Lampholders, and Lamps

    410.4 Luminaires in Specific Locations

    Part II. Luminaire Locations

    The text was modified in the 2005 Code to clarify the types of luminaires not permitted within 3 ft horizontally and 8 ft vertically from the top of the bathtub rim or shower stall. And new rule requires luminaires in bathtub or shower zone to be listed for damp locations, or listed for wet locations where subject to shower spray.

    (D) Above Bathtubs. No part of chain-, cable-, or cord luminaires, track lighting, or ceiling paddle fans is permitted to be located within 3 ft horizontally and 8 ft vertically from the top of the bathtub rim or shower stall threshold (bathtub/shower luminaire zone).

    Luminaires located in bathtub and shower zone must be listed for damp locations, or listed for wet locations where subject to shower spray.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  5. #5
    Join Date
    Jun 2010
    Posts
    43

    Default Re: Hanging light fixture above a tub?

    Thanks for your replies and (Fencepost) for the additional info. Very helpful.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •