    Default Re: Turning 30 amp 220 plug into standard single 20 amp outlet.

    Jack,
    Thank you. Just the type of info I was looking for. Just whe I thought of everything...I did not think about #8 fitting the breaker.
    And yes, the breaker will be sized to the smaller #12 wire used for the pigtail. Smallest wire used will be #12 on 20a breaker.
    Last edited by Rpm90001; 09-14-2013 at 01:40 PM.

  2. #12
    Join Date
    Apr 2012
    Posts
    25

    Default Re: Turning 30 amp 220 plug into standard single 20 amp outlet.

    Ok..my 20 amp breaker is rated for #14-#8 so #8 is no issue. So the only issue I could see that is out of the ordinary is the pig tail to the receptacle, and that's common practice. Looks like its a go.

    Thanks

    Geo

  3. #13
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    739

    Default Re: Turning 30 amp 220 plug into standard single 20 amp outlet.

    Quote Originally Posted by Rpm90001 View Post
    Ok..my 20 amp breaker is rated for #14-#8 so #8 is no issue. So the only issue I could see that is out of the ordinary is the pig tail to the receptacle, and that's common practice. Looks like its a go.

    Thanks

    Geo
    Rpm, there is no Code reason you can't do what you propose. In fact, if a 20A 120V run is several hundred feet long it is mandatory to do so, to reduce voltage drop.

    If the box behind the range is too small install a box extension (wll be on the surface of the wall), then your receptacle, so you don't have to jam your pigtail into a small box.
    Good Luck from Columbiana, Alabama
    Maurice Turgeon, Hidden Content

  4. #14
    Join Date
    Apr 2012
    Posts
    25

    Default Re: Turning 30 amp 220 plug into standard single 20 amp outlet.

    Maurice,
    Thank you, I was hoping you would chime in. The box should br large enough, but have a ring if needed

    Thank you,

    George

  5. #15
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    739

    Default Re: Turning 30 amp 220 plug into standard single 20 amp outlet.

    Quote Originally Posted by Rpm90001 View Post
    Maurice,
    Thank you, I was hoping you would chime in. The box should br large enough, but have a ring if needed

    Thank you,

    George
    Glad to help George, I do what you're planning all the time.
    Good Luck from Columbiana, Alabama