    This question is kinda tricky. So I'll try and do the best I can.

    OK, we bought a foreclosed house in Ohio about one month ago. It's a duplex that's about 90 years old. The house is doing well for the abuse it has been though being vacant for the last four years with winterization done after the fact.

    We have had the power on for almost a month now with no problems. Well the other night for some reason the lighting stopped working in the main bedroom, second floor hallway and Dinning room. Checked and none of the breakers have been tripped. Reset them all to make sure.

    Heres the tuff part. The Dinning room and second floor hall light have a switch on each floor. So two switches on the dinning room stair case and two in the hallway upstairs. After fishing around and knocking out the ceiling in the kitchen. There are five wires running close to one another. They run throught the joists going from the kitchen ceiling to the switches on the second floor down though the ceiling of the dinning room to the switches on the stair case.

    I have taken a multimeter and checked all the wires with of course no voltage. Now since there are five I am guessing one is the hot and rest are the neutral? Or is it one is neutral and one is hot? Whats also tied into this is the lighting for the back porch and ceiling power for the fan in the main bedroom also on the second floor.

    I can't seem to find where it starts and where it ends. As you guess it's the old knob and tube wiring. What also makes it hard is the breaker panel is new and tied into the old wiring at junction boxes. Where would be a good place to start looking?

    The place is going to be used for rental property. So I have a little time and would like to learn this. In other words I am not calling a electrician. LOL

    I can post some pictures if you like.

    Thanks,

    Mike

  2. #2
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,622

    Default Re: No Lighting in three areas.

    You haven't really supplied enough information. Generally with knob and tube you have a neutral runs and a hot runs.Depending on the age of the hose it could be one run each or several runs. The neutral run is generally taped to provide neutral to the outlets and light fixtures. The hot run is taped to provide hot to outlets (receptacles) and to switches from the switches a wire to the light fixtures. If you have 3-way switches hot to the first switch then two travelers to the second switch and a wire from the second to the lights.

    I would start at the panel and check for power from the breakers, then the junction box where the new is connected to the old and follow from there. Don't forget that an open neutral can also be the cause.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  3. #3
    Join Date
    Jan 2008
    Location
    Aurora, IL
    Posts
    12

    Default Re: No Lighting in three areas.

    I have run into, more often than not actually, they actually switch the neutral instead of the hot at the switch. Makes life more confusing.

    Knob and tube can be some of the hardest wiring to troubleshoot because it generally isn't marked and many splices are not made in boxes, but...well...wherever the original electrician wanted to. You may be scratching your head for hours, days, or weeks. I'd employ a licensed electrician for this one.