    NEC 210.52 (D) Bathrooms. In dwelling units, at least one receptacle
    outlet shall be installed in bathrooms within 900 mm (3 ft)
    of the outside edge of each basin. The receptacle outlet
    shall be located on a wall or partition that is adjacent to the
    basin or basin countertop, or installed on the side or face of
    the basin cabinet not more than 300 mm (12 in.) below the
    countertop.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  2. #12
    Join Date
    Dec 2010
    Location
    Houston Texas
    Posts
    3,201

    Default Re: Electrical Outlet in the bathroom

    But the secondary and subsequent outlets can be anywhere.

  3. #13
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,115

    Default Re: Electrical Outlet in the bathroom

    Quote Originally Posted by HoustonRemodeler View Post
    But the secondary and subsequent outlets can be anywhere.
    True and I can find no reference to 42".

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  4. #14
    Join Date
    Dec 2010
    Location
    Houston Texas
    Posts
    3,201

    Default Re: Electrical Outlet in the bathroom

    That might fall under ADA reach rules, but as long as there is more than one or the outlet is for a purpose, then all bets are off.

  5. #15
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    843

    Default Re: Electrical Outlet in the bathroom

    Quote Originally Posted by JLMCDANIEL View Post
    NEC 210.52 (D) Bathrooms. In dwelling units, at least one receptacle
    outlet shall be installed in bathrooms within 900 mm (3 ft)
    of the outside edge of each basin. The receptacle outlet
    shall be located on a wall or partition that is adjacent to the
    basin or basin countertop, or installed on the side or face of
    the basin cabinet not more than 300 mm (12 in.) below the
    countertop.

    Jack
    Jack a ROP reworded it a bit:

    Recommendation: Revise text to read as follows:
    (D) Bathrooms. In dwelling units, at least one receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin. The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop, located on the countertop, or installed on the side or face of the basin cabinet. In no case shall the receptacle be located not more than 300 mm (12 in.) below the countertop top of the basin. Receptacle outlet assemblies listed for the application shall be permitted to be installed in the countertop.

    The only other restriction for bathrooms:

    (C) Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall.
    Good Luck from Columbiana, Alabama
    Maurice Turgeon, Hidden Content