    I recently had half my basement finished by contractors. I just tried to plug in a small space heater and shortly there after my electric turned off. what does this mean?

  2. #2
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,080

    Default Re: Breaker in circuit panel box keeps popping

    One circuit or the whole house? If it was one breaker, what was the rating of the breaker, how many watts was the heater, and what else was plugged into the circuit?
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  3. #3
    Join Date
    Mar 2009
    Location
    Ma
    Posts
    9

    Default Re: Breaker in circuit panel box keeps popping

    why didn't you have heat installed? space heaters are not good.. probably overloaded the circuit..or maybe they wired it to an arc fault breaker check to see if it needs to be reset

  4. #4
    Join Date
    Jan 2009
    Location
    Truckee, Calif.
    Posts
    24

    Default Re: Breaker in circuit panel box keeps popping

    Ohm's Law....amps = watts / volts.... so if your heater is rated at 1500 watts and 120 volts (standard plug), then you would be drawing 12.5 amps just for the heater. Add a few lights, TV, etc. and you can easily exceed the breaker rating. Using an exetnsion cord with the heater will make matters worse. Most breakers trip at 125% of rating. Don't assume a bad breaker. It's probably preventing you from setting your house on fire.
    Just because you can, it doesn't mean you should!

  5. #5
    Join Date
    Feb 2009
    Posts
    693

    Default Re: Breaker in circuit panel box keeps popping

    Quote Originally Posted by Vern Smith View Post
    Ohm's Law....amps = watts / volts.... so if your heater is rated at 1500 watts and 120 volts (standard plug), then you would be drawing 12.5 amps just for the heater. Add a few lights, TV, etc. and you can easily exceed the breaker rating. Using an exetnsion cord with the heater will make matters worse. Most breakers trip at 125% of rating. Don't assume a bad breaker. It's probably preventing you from setting your house on fire.

    I sure like this post. Agree as well.

  6. #6
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,904

    Default Re: Breaker in circuit panel box keeps popping

    Using an extension cord won't increase the load on the circuit. What it will do is increase the resistance, lowering the effective voltage & wattage of the heater (and thereby lower the amperage draw). Using an extension cord with a heater is a big no-no because the heavy load of the heater tends to be more than the extension cord is rated for; the cord itself may overheat and start a fire.

    My advice to everyone: when the walls are open, install more wires & circuits than you think you'll need. You'll need them, and it's cheaper to install sooner than later.

    Edit: a breaker may trip at around 125% of rating after a short period of time, but it will allow probably a 200% draw for a fraction of a second (to allow for motor loads starting up) and may trip at only 105% over a long period of time. Many breakers use both thermal and a magnetic trip; the thermal handles the long-term-slight-overload to protect from having too much on the circuit, and the magnetic handles the short-term-high-overload to protect from short circuits.
    Last edited by Fencepost; 04-24-2009 at 01:58 AM.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.