    Howdy consider having an electrician come and bid the job. Did you pull a permit? I ask as its getting harder to ever sell a home without permitted improvements. Consider getting a books on basic wiring. Good workmanship and code mandates proper spacing and sizing of the lighting,outlets, wire, fasteners, boxes, GFRI recepticles ... a whole host of items to ensure safe construction.

  2. #12
    Join Date
    Jun 2007
    Location
    Shamokin, Pa.
    Posts
    645

    Default Re: how many outlets and lights

    Quote Originally Posted by NEC View Post
    Could be, I guess. It would mean though that you could put every single receptacle in a home in a home on a single circuit, not limited by other NEC resrictions and meet the requirements of the NEC.
    True but I always use the number eight as a cut off point. Once again no exact reason why using that number.

  3. #13
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: how many outlets and lights

    Quote Originally Posted by jkirk View Post
    gotta love the canadian code eh canuk. wheres old brpw to argue this topic when needed
    Yep ... .....
    "" an ounce of perception -- a pound of obscure "
    - Rush

  4. #14
    Join Date
    May 2009
    Posts
    2

    Default Re: how many outlets and lights

    Quote Originally Posted by JLMCDANIEL View Post
    Voltage drop calculations are dependent on wire size, voltage, and load. As a general rule of thumb if you run over 100 feet you would go to the next size wire however for incandescent lights the only effect of the voltage drop would be slightly dimmer lights. There is no real code restrictions on length of run or allowable voltage drop.
    I would suggest however that you run 12 ga (20 amp circuit) rather than 14ga for the outlets and have that separate from the lighting circuits. That way if you pop a breaker you won't be completely in the dark.
    Jack

    Oh, yes their is a NEC code about voltage drop. No more than 3% on branch circuits and no more than 5% on service and branch circuits.

    As a rule. No more than 10 outlets on a circuit. Far as #14 AWG. Use #12. #14 is just control wire. You'll never see a union electrician use #14.

  5. #15
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    5,557

    Default Re: how many outlets and lights

    Quote Originally Posted by Union Sparkie View Post
    Oh, yes their is a NEC code about voltage drop. No more than 3% on branch circuits and no more than 5% on service and branch circuits.

    As a rule. No more than 10 outlets on a circuit. Far as #14 AWG. Use #12. #14 is just control wire. You'll never see a union electrician use #14.
    Actually there is not an NEC code, there is onlt a FPN (fine print note) An FPN is not a code requirement.
    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  6. #16
    Join Date
    Jun 2007
    Location
    Shamokin, Pa.
    Posts
    645

    Default Re: how many outlets and lights

    Quote Originally Posted by Union Sparkie View Post
    Oh, yes their is a NEC code about voltage drop. No more than 3% on branch circuits and no more than 5% on service and branch circuits.

    As a rule. No more than 10 outlets on a circuit. Far as #14 AWG. Use #12. #14 is just control wire. You'll never see a union electrician use #14.
    Very few non-union as well

  7. #17
    Join Date
    Nov 2007
    Posts
    980

    Default Re: how many outlets and lights

    union does does not denote quality it denotes unity

  8. #18
    Join Date
    Feb 2009
    Posts
    693

    Default Re: how many outlets and lights

    Jack is 100% correct on the voltage drop issue...... As a union electrician I pulled miles of #14 in residential applications.

    We just stuck to a rule of 8 receptacles on a 15 amp circuit and 10 on a 20. Pretty simple in that 180va is allowed for each receptacle either way.