Results 1 to 10 of 17
    240
    Default Do I Need A Ground Rod
    My breaker box connects to ground by a wire connected to nearby copper piping. Do I need to install a new grounding rod or would I get any additional protection if I did?
    Aug 2011
    Northern Indiana
    111
    Default Re: Do I Need A Ground Rod
    Is the copper pipe connection a grounding electrode connection or just a bonding connection? To be a grounding electrode the connection should be made within 5' of where the metallic pipe enters the structure. And yes, there should be supplemental rods for the service.
    The last time I ask my electrician this question, he said yes.
    Dec 2011
    Cressona, PA
    You need a minimum of 2 grounding electrodes. The water pipe counts as 1, so you need 1 more.
    May 2011
    251
    You can't really have too many. The water service pipe is still the best ground because of it's depth underground. But I'd still want 2 near the box so that you have a localized ground right near the main service entrance. The ground potential can still vary over even a few feet. Additionally, you still want your plumbing grounded... especially if you have copper or galvanized pipes. Although those in old hoses often have a ground for their plumbing already since all the drain pipes are iron.
    Funny how a lot of the new and supposedly superior products can often create new issues. With all PVC and plastic pipes, you lose that ability to ground your plumbing. Perhaps it's not needed as much in that case. Personally, I still have doubts that PEX & PVC will last longer than the 86 y/o steel and 65 y/o copper that still in service. We'll see.
    Aug 2011
    Northern Indiana
    111
    Quote Originally Posted by motoguy128 View Post
    Bonding the metallic piping systems has nothing to do with grounding. The purpose of bonding is to provide a low impedance path wihich will allow circuit breakers to trip in the event the piping becomes electrically energised.
    Columbiana, Alabama
    843
    If your service entrance panel was connected to the metal water pipe within 5 ft of the point it enters the house and 10 ft of it is in contact with the soil you have one of the best grounding electrodes available.
    However, as was mentioned, you still need two more (spaced at least 6 ft apart from the each other), unless you measure you measure the effectiveness of the first rod and it measures at least 25 ohms.
    As was also mentioned metal piping and duct work should all be connected by at least #6 copper wire.
    Maurice Turgeon, http://thesemi-retiredelectrician.com
    1,901
    Quote Originally Posted by The Semi-Retired Electric View Post
    Besides water piping, this also includes gas piping and even metal building framing. If there are sections of metal piping separated by plastic, it's necessary to connect each section of metal piping as well.
    Maurice, what about dielectric unions? The purpose of them is to electrically separate copper and galvanized steel piping to prevent electrolysis, but it seems that doing an electrical bond as required by the electrical codes would defeat the purpose of the dielectric union (as required by plumbing codes). Are the different codes at odds with each other?
    May 2011
    251
    Good point about ductwork. While the case of the furnace or air handler is usually grounded, that's not a very large ground wire. Probably best to have a separate ground connected to any nearby copper water piping. Probably wouldn't hurt to do this in a couple places where convenient.
    I just added another thing to my to-do-list.
    Aug 2011
    Northern Indiana
    111
    Please show me where the electrical code requires duct work to be bonded