+ Reply to Thread
Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2009
    Posts
    240

    Default Switch Box Options For Box Fill Limitations

    My original plan was to wire my bedroom with a new circuit for lighting/ceiling fan and one additional receptacle but i seem to be struggling with figuring out code limitations on box fill.

    I was planning on using 14/2 to feed the switch first(so i have my neutral for 2011 code) and use 14/3 to feed the light/fan. I was then planning on pigtailing from the light switch to feed the receptacle then feed from the receptacle to a different light switch for a closet light.

    Problem is as the main light switch I would have:
    14/2 feed from breaker = 3 conductors counting ground
    14/3 feed to ceiling fan = 4 conductors counting ground
    14/2 feed from switch to receptacle = additional 3 conductors counting ground
    For a total of 10 conductors in the switch box and if I have to include the pigtails, that's another 3.

    I'm certain that i'm doing something wrong here or maybe overthinking it but I have no idea how i'm suppose to do this if a standard metal switch box has a limit of 5 14-gauge conductors as listed in NEC table 314.16. Am I misinterpreting the code here?
    My advice and opinions come from hands on knowledge...and This Old House Hidden Content

  2. #2
    Join Date
    Mar 2009
    Posts
    240

    Default Re: Switch Box Options For Box Fill Limitations

    From what iv'e read, this is what i have so far

    14/2 feed from breaker = 2
    14/3 feed to ceiling fan = 3
    14/2 feed from switch to receptacle = 2
    This gives me 7 conductors + 1 for ground + 1 for cable clamps + 2 for strap/yoke for switch = 11 conductors

    Any wiring or box suggestions?
    Last edited by dcalabro; 12-02-2011 at 02:18 PM.
    My advice and opinions come from hands on knowledge...and This Old House Hidden Content

  3. #3
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,047

    Default Re: Switch Box Options For Box Fill Limitations

    First of all you need to use 12 gage, you need a 20 amp circuit for bathe rooms. I don't recommend lights and receptacles on the same circuit because a hair dryer could trip breaker and leave you in the dark but

    Run 12/2 to first receptacle, 12/2 to second receptacle, 12/2 from number 2 receptacle to light fan, and 12/4 from light fan to switch box.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  4. #4
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    843

    Default Re: Switch Box Options For Box Fill Limitations

    If I start to fill up a 3 gang box with devices and wire I just go with a 4 gang for space and install a filler plate over one of the deco openings.

    Good Luck from Columbiana, Alabama
    Maurice Turgeon, http://thesemi-retiredelectrician.com

  5. #5
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,047

    Default Re: Switch Box Options For Box Fill Limitations

    Oops, sorry . Fpr some reason I read bathroom.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •