    Is there a best practice for the wiring order if connecting a light switch and electrical outlet on the same circuit? For example should the feed from the breaker go to the light switch first or the outlets? The reason i ask is because in one room the light dims when i use my drill.
    Default Re: Best practice wiring order
    To be honest, I don't think it matters how you wire the switches and outlets on a circuit, though lighting and outlets are supposed to be on separate circuits so that when you overload an outlet and blow a breaker, you don't lose your lighting to find your way to reset it.
    Whether or not you can eliminate flickering/dimming is questionable, I think it has more to do with how the circuits are wired at the panel than how they are connected throughout the house.
    1,904
    Even though it's permissible, I don't like the idea of feeding a circuit through a receptacle (where the incoming wire connects to one screw and the outgoing wire connects to another). I prefer to connect the wires with a wire nut, with a single pigtail to the receptacle.
    I'm not sure why I feel this way, it just seems like a better way to do it for some reason.
    Try plugging your drill in other places. Do you get the same dimming?
    6,075
    An excessively long run of undersized wiring is most likely the problem. While it may be a 15 amp circuit line drop may have been taken into consideration.
    Columbiana, Alabama
    843
    With 2011 Code a neutral must now be present in every branch circuit switch location, even if it's not being used, with very few exceptions. This is to allow use of an occupancy sensor in the future.
    So, running power to the switch location is now a smart move. If you have a 3 way or 4 way switch circuit you either have to run 4 wire romex or MC cable etc. or supply power to the other 3 way (and 4 ways), from the same branch circuit.
    This of course has nothing to do with your dimming problem.
    Maurice Turgeon, http://thesemi-retiredelectrician.com
    240
    ***, a few pieces of information here.
    Voltage drop is something I did not take into account here. I know the current light and outlet are on a 15a running over knob and tube.I am planning on upgrading the room with this problem to be on its own 20a circuit for the outlets and the light on a 15a to phase out the k&t.
    My question now applies to voltage drop because the branch feed from the breaker to the first outlet on the 20 amp circuit will be about 50 ft then another 10 feet to the last outlet for that circuit. Am I ok with 12ga or should I be running 10ga to the first outlet then use 12ga to branch off to the remaining 2 outlets?
    Same question applies for the 15a lighting circuit, same 50ft branch to switch but then about 20ft for lighting of ceiling fans in other rooms. I'm now thinking I should use 12ga throughout for this but would I be ok with 14/2?
    Regarding the 2011 code adjustments. I planned on running power directly to the switch with lets say 12/2 then I will run 12/3 from switch to ceiling fan to assume separate control of fan vs light. Don't I already have the neutral from the feed at the switch or are you saying that the 12/3 needs to be 12/4?
    Quote Originally Posted by dcalabro View Post
    Ah -- that explains a lot.
    You're fine with the 12 ga. -- no need to go larger.
    You're fine with the 14 ga
    You're fine running the supply feed to the switch location because the neutral will be there. This is my perfered method of running a circuit for a light .
    Columbiana, Alabama
    843
    I've been running 12-4 rather than 12-3 between 3 way switches so I'd have a neutral in both boxes, which is now required.
    But,there are other ways to do it
    Maurice Turgeon, [URL="http://thesemi-retiredelectrician.com"]
    6,075
    Generally speaking voltage drop doen't come into play unless your run is over 100 feet, or a heavy load is used. Ths can easily happen with a single 15 amp circuit feeding multiple lights and recepticles.
    You should have no proble with 12 ga here
    Again you should have no problem here.
    In this case you would have the required neutral at the switch.