    Default Re: Meter base problem?

    Sam, if you don't have any dairy farms in the city..how do you have freshmilk?

    I guess you have SWER in the country as well, since the rural areas would save the most money on transmission lines. Glad to hear they don't have problems as well.

    Maurice

  2. #22
    Join Date
    Dec 2015
    Posts
    1

    Question Re: Meter base problem?

    So, will a burnt connection, in the meter base, on the right upper connection, from a feed line..., cause an increase in your electric bill? (if so, can this be due to higher current draw or something else?)

    Thanks, I would REALLY Appreciate any answers!

    Danny

  3. #23
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,015

    Default Re: Meter base problem?

    Quote Originally Posted by danielosko View Post
    So, will a burnt connection, in the meter base, on the right upper connection, from a feed line..., cause an increase in your electric bill? (if so, can this be due to higher current draw or something else?)

    Thanks, I would REALLY Appreciate any answers!

    Danny
    Yes, burnt connections cause a high resistance. Usually cause by loose connection.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  4. #24
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,884

    Default Re: Meter base problem?

    Quote Originally Posted by danielosko View Post
    So, will a burnt connection, in the meter base, on the right upper connection, from a feed line..., cause an increase in your electric bill? (if so, can this be due to higher current draw or something else?)

    Thanks, I would REALLY Appreciate any answers!

    Danny
    No, it cannot cause an increase in your electric bill. Electric meters are passive serial devices, meaning that they measure current passing through them. Electric meters do consume a negligible amount of electricity. If there is nothing using electricity on the downstream side of the meter, there is no current to pass through the meter. A burnt connection will increase the resistance in the line, which will reduce the voltage and therefore the current flowing through the meter.

    A burnt connection should be replaced. It is a fire hazard; it can result in overheating and arcing (when a load is applied) which can damage insulating materials in the meter base and potentially cause ignition of nearby materials outside of the meter base. The arcing can also damage sensitive electronic components.

    The upper contacts of a meter base are on the utility side of the meter. If, somehow, there is current leakage from the upper contacts, the meter will not measure it. Current leakage on the lower contacts would be measured, as that is on the "downstream" side of the meater.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  5. #25
    Join Date
    Jun 2007
    Location
    Fayette County, Ohio
    Posts
    6,015

    Default Re: Meter base problem?

    Even higher resistance on the utility side increases the total resistance in the circuit. The voltage stays the same, more resistance means more current .

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  6. #26
    Join Date
    Aug 2011
    Location
    Northern Indiana
    Posts
    103

    Default Re: Meter base problem?

    Quote Originally Posted by JLMCDANIEL View Post
    Even higher resistance on the utility side increases the total resistance in the circuit. The voltage stays the same, more resistance means more current .

    Jack
    I=V/R
    If the voltage remains the same how does increasing resistance increase the current?
    A 120 volt circuit with a 10 ohm resistive load has a current of 12 amps. With a 20 ohm load the current is 6 amps.
    Last edited by brrichter; 12-04-2015 at 11:31 PM.

  7. #27
    Join Date
    May 2008
    Location
    Pacific Northwet
    Posts
    1,884

    Default Re: Meter base problem?

    Quote Originally Posted by brrichter View Post
    I=V/R
    If the voltage remains the same how does increasing resistance increase the current?
    A 120 volt circuit with a 10 ohm resistive load has a current of 12 amps. With a 20 ohm load the current is 6 amps.
    If you ADD a resistive load in parallel (for example, you plug in a space heater), you DECREASE the total resistance. So two 10 ohms loads in parallel drawing 12 amps each results in a 5 ohm total load drawing 24 amps.

    But if you add the resistive load in series, you INCREASE the total resistance. So two 10 ohm loads in series results in a 20 ohm total load drawing only 6 amps.

    The resistance presented by a burnt contact is in series with the load, not in parallel. Therefore, the total resistance increases, decreasing the current flow.

    Please pardon me for confusing the issue with facts and logic.
    The "Senior Member" designation under my name doesn't mean I know a lot, it just means I talk a lot.I've been a DIYer since I was 12 (thanks, Dad!). I have read several books on various home improvement topics. I do not have any current code books I can refer to. I was an apprentice plumber for two years.

  8. #28
    Join Date
    Jan 2008
    Posts
    2,684

    Default Re: Meter base problem?

    Rather than argue the details, I say just replace the meter box for safety purposes. Sometimes the utility company will do this for free or at a low price and sometimes you will need to have an electrician do this. Check with your utility company to find out. A burned-down house is not an option here and I promise it is more costly than any increase in your power bill ever could be whether that is happening here or not. And I=V/R doesn't apply here; Ohm's law is different with AC current http://www.zen22142.zen.co.uk/Theory/ohmac.htm

    Phil

  9. #29
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    843

    Default Re: Meter base problem?

    We've seen a bunch of good suggestions. IMO the key was in the original post where the neutral was compromised due to a loose connection.

    The lug was replaced but no mention if the wire was trimmed back, per accepted good practice, before it was hopefully re-torqued. A manufacture was offering a $100 to a group of inspectors and contractors who could properly torque a lug without a torque wrench. They gave away very little money. I then dusted off my torque wrenches.

    The OP said numerous appliances were damaged and replaced. I suspect some are still arcing away at random such as the heat pump and the electric water heater.

    These can go undetected except when you see a high power bill.

    Since the meter stops when the main breaker is "off" turning all the breakers "off" one at a time and watching the meter, as many have suggested, should find the culprit(s).
    Good Luck from Columbiana, Alabama
    Maurice Turgeon, Hidden Content