    Quote Originally Posted by canuk View Post
    Providing there is one neutral and 2 hot legs --- there will be 1-220/240 volt circuit and/or 2- 110/120 volt circuits.

    Two neutrals are not required.
    Only one neutral required.

    Jack
    Be sure you live your life, because you are a long time dead.-Scottish Proverb

  2. #12
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: Wiring

    Quote Originally Posted by JLMCDANIEL View Post
    Only one neutral required.

    Jack
    Ummm -- yep and agreed.
    "" an ounce of perception -- a pound of obscure "
    - Rush

  3. #13
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    708

    Default Re: Wiring

    It's already been mentioned but the two 120 volt circuits must be on separate phases.

    One must install a two pole breaker to ensure this. And yes only one neutral, two would be a Code violation.

    Good Luck from Columbiana, Alabama
    Maurice Turgeon, thesemi-retiredelectrician.com