    Default Closed-cell spray insulation near water heater exhaust

    I am having my garage ceiling sprayed with closed-cell insulation. My water heater is in the garage and the exhaust vent goes through the ceiling through the room above and out the roof. Question is, when they spray my ceiling, can they spray right up to the exhaust vent?

  2. #2
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: Closed-cell spray insulation near water heater exhaust

    Your insulation contractor should know the code.
    Generally, if the exhaust pipe is a *B* vent then insulation not fire rated can be within around 1 inch. If the exhaust pipe is a single wall *C* vent then non fire rated insulation can't be closer than around 6 inches.
    This will vary by local building codes.
    "" an ounce of perception -- a pound of obscure "
    - Rush

  3. #3
    Join Date
    Mar 2011
    Posts
    5

    Default Re: Closed-cell spray insulation near water heater exhaust

    My water heater is in the garage and the exhaust vent goes through the ceiling through the room above and out the roof.