    Default want to run electric from basement to attic

    can anyone tell me what is the propular wiring to run and what fuse to the box

  2. #2
    Join Date
    Aug 2007
    Location
    The Great White North
    Posts
    4,045

    Default Re: want to run electric from basement to attic

    When you apply for the permit that information will be provided .
    "" an ounce of perception -- a pound of obscure "
    - Rush

  3. #3
    Join Date
    Jan 2011
    Location
    Columbiana, Alabama
    Posts
    710

    Default Re: want to run electric from basement to attic

    What kind of load do you want to run in the attic?

    If it's just a fan and a few lights 12#-2 romex with a ground should work fine.

    You will need to install a 20A fuse or breaker.

    Maurice Turgeon, thesemiretiredelectrician.com

  4. #4
    Join Date
    Mar 2009
    Location
    wisconsin
    Posts
    159

    Default Re: want to run electric from basement to attic

    you are going to have to find out your ordinances here. a 12/2 would probably be sufficient, however certin locations require all wiring to be in conduit such as emt, or fmc. you will need to know what is required in your area.